Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

How to Change Active Alarm Status to Resolved

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How to Change Active Alarm Status to Resolved
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
76
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:11 PM

0 Likes
5
510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 08:11 PM

How to Change Active Alarm Status to Resolved

This question was originally posted on DCIM Support by Shaik Mahboob Ali on 2019-06-24


Hi Team,

Need support to remove  fake "Active Alarm" from UPS device through DCE system. Please see attach UPS device without any Active Alarm but still there is Active alarms in the history without resolved. Can we change status as "resolve" from "Active"  through any configuration change. Your quick reply is highly appreciated.

  

(CID:145851117)

Labels
  • Labels:
  • Data Center Expert
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:12 PM

0 Likes
0
512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 08:12 PM

This answer was originally posted on DCIM Support by spezialist on 2019-06-24


Dear Shaik Mahboob Ali,

From your comments:

...and i have change the ddf with correct one then my device alarm working perfectly but this alarm still exist as " Active and As per UPS device PPM there is no alarms & i have hidden it.

This means, that your changes to the DDF-file were not as correct as you think (there is an error in the DDF-file). To check this, you need to remove your problem device from DCE and discover it again.

Therefore, if there are really no alarms on your device, then you need to find your device on the DDF resource and make the corresponding Request modification. And then you will receive a truly correct DDF-file.

Hope this helps you.

With respect.

(CID:145851205)

See Answer In Context

Reply
Share
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:12 PM

0 Likes
1
512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 08:12 PM

This answer was originally posted on DCIM Support by spezialist on 2019-06-24


Dear Shaik Mahboob Ali,

I suspect that this is not fake alarms, but active alarms. Just someone has hidden them (hidden alarms are displayed in italics). To see them, you just need to click on the Show Hidden Alarms button as in my screenshot:

Since these alarms are active, you cannot simply give resolved status for understandable reasons. If the alarms are active, then you have problems on the device, and as long as you do not solve them there, the alarms will not be resolved.

Very thanks for the support.

(CID:145851138)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:12 PM

In response to DCIM_Support
0 Likes
0
512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 08:12 PM

This comment was originally posted on DCIM Support by Shaik Mahboob Ali on 2019-06-24


Hi Thanks for your quick reply. Your are right but there was a problem with DDF of this device , as this same alarm was continuously triggering and i have change the ddf with correct one then my device alarm working perfectly but this alarm still exist as " Active and As per UPS device PPM there is no alarms & i have hidden it. so is there any way to clear this alarm.

(CID:145851171)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:12 PM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 08:12 PM

This answer was originally posted on DCIM Support by spezialist on 2019-06-24


Dear Shaik Mahboob Ali,

From your comments:

...and i have change the ddf with correct one then my device alarm working perfectly but this alarm still exist as " Active and As per UPS device PPM there is no alarms & i have hidden it.

This means, that your changes to the DDF-file were not as correct as you think (there is an error in the DDF-file). To check this, you need to remove your problem device from DCE and discover it again.

Therefore, if there are really no alarms on your device, then you need to find your device on the DDF resource and make the corresponding Request modification. And then you will receive a truly correct DDF-file.

Hope this helps you.

With respect.

(CID:145851205)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:12 PM

0 Likes
0
514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 08:12 PM

This answer was originally posted on DCIM Support by Haleem Malik on 2019-06-24


Hi Shaik,

If there is no any active alarm present physically at UPS web page then definitely it is DDF issue, send back to development team and ask them to amend.

 

BR,

Haleem Malik

(CID:145851323)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:12 PM

0 Likes
0
514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 08:12 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Share
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc