How do I mass configure APC devices using Data Center Expert?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How do I mass configure APC devices using Data Center Expert?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:11 PM . Last Modified: ‎2024-04-07 11:57 PM

0 Likes
1
1204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:11 PM . Last Modified: ‎2024-04-07 11:57 PM

How do I mass configure APC devices using Data Center Expert?

Note: If you wish to mass configure user settings, please go here.

1) Open the Data Center Expert Desktop Client and log in.


2) Within the Monitoring Perspective (button) select the group that contains the devices within the Device Groups pane.  Within the Device View pane, right-click on the device and select APC SNMP Device Configuration.
NOTE: An alternative method is to go to the Device menu and select APC SNMP Device Configuration.

3) If prompted to select a Configuration Type, select Standard device configuration settings and click OK.
NOTE: You will only be prompted to select a Configuration Type if the device that was right-clicked on is running firmware version 6.X or higher.

4) Select Configure Devices.

5) Select a device from the list and then select Retrieve Device Settings.
NOTE: If you receive an error message, see steps at bottom of knowledge base to resolve.

6) Once the settings are retrieved, select Next.

7) Check the boxes of the devices that you wish to configure the same settings on and select Next. 
TIP: You can use the Select/Deselect All check box to uncheck the list of devices.
NOTE: You can not choose unique settings per device.  This option is to push the same settings out to all selected devices.
NOTE: It is recommended to test this with a single device before mass configuring more than one device.

😎 Navigate through the tree of items to find the settings you are looking for.
NOTE: Do not select the root tree item.  Only select the individual items that you wish to mass configure.

9) Select the line item for the setting and then select the Edit button.

10) Change the value to what is required and click OK.

11) Once all of the settings that you wish to change are edited, click Finish.

12) The Device Configuration Status pane will automatically load and show the progress of each of the transfers.

  • Step 1: Retrieving configuration...
  • Step 2: Transferring configuration...
  • Step 3: Waiting for configuration to load...
  • Step 4: Retrieving configuration...
  • Step 5: Configuration successful or Incomplete configuration

NOTE: A Status of Incomplete configuration does not indicate that the changes failed.  Right-click on the line item and select View Configuration Results.  See the Error Messages section below for additional details.

NOTE: If you have changed FTP or SSH (SCP) settings, DCE may be unable to verify the changes.  Please ensure to edit the Device File Transfer settings to contain the new protocol settings.

Error Messages

Incomplete Configuration
The configuration finished, but not all settings were applied successfully or able to be verified.  Right-click on the line item within the Device Configuration Status pane and select Show Configuration Results.  If the actual value says Not Supported, it indicates that either the device does not support the value or the value is unable to be verified for security reasons.

Failed: Unable to connect
A network or file transfer protocol communication problem exists.  Make sure the device is turned on and online, the appropriate file transfer protocol is enabled at the device, and that the "Device File Transfer Settings" used to access the device include the device's correct port number.

Failed: Unable to log on
The StruxureWare Data Center Expert server does not have the appropriate file transfer protocol settings needed to log on to the device, or communication was lost after the connection was successful.  Make sure the access settings needed to log on to the device are defined in the "Device File Transfer Settings" display, and the appropriate file transfer protocol is still enabled at the device.

Failed: Unable to retrieve configuration
A problem occurred, after the StruxureWare Data Center Expert server transferred the configuration to the device successfully, that prevented the server from verifying that the configuration was successful by retrieving a copy of the configuration from the device.  Make sure that the device has not been turned off or disconnected from the network, access settings have not changed at the server or device, and the appropriate file transfer protocol is still enabled at the device.

Failed: Connection timed out
A network or file transfer protocol communication problem prevented the StruxureWare Data Center Expert server from logging on before the Timeout identified in the "Device File Transfer Settings" display expired.  Make sure the device is turned on and online, and the appropriate file transfer protocol is enabled at the device.  Also, make sure the "Device File Transfer Settings" display includes the correct access settings needed to access the device, and that the Timeout value is appropriate for the network traffic requirements.

Editing Device File Transfer Settings

1) On the select Destination Devices screen, click the Device File Transfer Settings Button.

2) Either Add a new entry or Edit an existing entry.
NOTE: It is recommended to keep the number of entries to a minimum.
NOTE: It is recommended to have as few wildcard entries as possible that apply to the same device ranges.

3) Ensure to select the appropriate IP range, username, password, and protocol type for the device connection.

(CID:122691988)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • NMC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:12 PM . Last Modified: ‎2023-10-22 02:21 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:12 PM . Last Modified: ‎2023-10-22 02:21 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore