How do I add devices to StruxureWare Data Center Expert?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How do I add devices to StruxureWare Data Center Expert?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:04 AM . Last Modified: ‎2024-04-10 01:47 AM

0 Likes
3
4747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:04 AM . Last Modified: ‎2024-04-10 01:47 AM

How do I add devices to StruxureWare Data Center Expert?

I would like to add a number of devices to my StruxureWare Data Center Expert setup. What is the process for adding devices that can then be monitored?

(CID:83656825)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:04 AM . Last Modified: ‎2024-04-10 01:47 AM

0 Likes
0
4744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:04 AM . Last Modified: ‎2024-04-10 01:47 AM

You can add devices by going to “Device-> Add Devices…” in the Data Center Expert client or by right clicking in the monitoring perspective and choosing "Add Devices". Before doing so, there is some basic information you should have about the device(s) to be discovered. 

The types of devices you can discover are: 
SNMPv1
SNMPv3
Nebotz Appliance
Modbus TCP

Things to know before adding an SNMPv1 device.
The device’s IP address or IP subnet the device(s) are on.
The SNMP community strings of the device(s).
The NMS IP restrictions associated with those community strings

Things to know before adding an SNMPv3 device.
The device’s IP address or IP subnet the device(s) are on.
SNMPv3 Username and Authentication / Encryption type if they are enabled
Authentication and Encryption passwords
Make sure the User that you are using is enabled.

Things to know before adding a Netbotz Appliance device.
The device’s IP address or IP subnet the device is on.
Nebotz Administrative Username and password.
If the device is using HTTP or HTTPS and which ports it is using.

Things to know before adding an ModbusTCP device.
The device’s IP address OR the IP of ModbusTCP gateway connected to the device
The slave address of the device
If a Modbus gateway is being used making sure the gateway can communicate to the Modbus device prior to discovery may be helpful as well.

Tips when adding any device
Make sure to hit the Next key instead of the Finish key until next is not available. There is an option to “run discover now” which is often missed. If you do finish the discovery creation without checking this box you can right click on the discovery under the “Saved Discoveries” tab and chose the run option.

Make sure the correct Device Definition File (DDF) for the device(s) has been uploaded to DCE (Data Center Expert). APC devices should have pre-loaded DDF files but 3rd party devices may need to be loaded manually. To upload or verify the Modbus DDF, go to “Device > Modbus Device Communication Settings> Device Definition Files”. To upload or verify an SNMP DDF, go to “Device > SNMP Device Communication Settings> Device Definition Files”. If the correct DDF is not present please contact your local tech support. Tech support may be able to provide a DDF or, if a new DDF needs to be created for your specific device, they can get you in touch with a team that creates these files.

For DCE version 7.2.x and above, you can send devices to a specific group during discovery. Make sure to take note of which group you are adding the device.

If the device is not showing up after running the Discovery 
Try highlighting the “All devices” group and searching for the devices IP under the “Device View” tab to make sure it did not add under a different folder. You can usually either find the device by IP or hostname. 

Check the logs on the device to see if there are any unauthorized attempts to access the device. If there are unauthorized attempts listed the credentials being used(ex. SNMPv1 community strings or SNMPv3 User information) may be incorrect in your discovery. 

(CID:83656827)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:04 AM . Last Modified: ‎2024-04-10 01:47 AM

0 Likes
0
4745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:04 AM . Last Modified: ‎2024-04-10 01:47 AM

You can add devices by going to “Device-> Add Devices…” in the Data Center Expert client or by right clicking in the monitoring perspective and choosing "Add Devices". Before doing so, there is some basic information you should have about the device(s) to be discovered. 

The types of devices you can discover are: 
SNMPv1
SNMPv3
Nebotz Appliance
Modbus TCP

Things to know before adding an SNMPv1 device.
The device’s IP address or IP subnet the device(s) are on.
The SNMP community strings of the device(s).
The NMS IP restrictions associated with those community strings

Things to know before adding an SNMPv3 device.
The device’s IP address or IP subnet the device(s) are on.
SNMPv3 Username and Authentication / Encryption type if they are enabled
Authentication and Encryption passwords
Make sure the User that you are using is enabled.

Things to know before adding a Netbotz Appliance device.
The device’s IP address or IP subnet the device is on.
Nebotz Administrative Username and password.
If the device is using HTTP or HTTPS and which ports it is using.

Things to know before adding an ModbusTCP device.
The device’s IP address OR the IP of ModbusTCP gateway connected to the device
The slave address of the device
If a Modbus gateway is being used making sure the gateway can communicate to the Modbus device prior to discovery may be helpful as well.

Tips when adding any device
Make sure to hit the Next key instead of the Finish key until next is not available. There is an option to “run discover now” which is often missed. If you do finish the discovery creation without checking this box you can right click on the discovery under the “Saved Discoveries” tab and chose the run option.

Make sure the correct Device Definition File (DDF) for the device(s) has been uploaded to DCE (Data Center Expert). APC devices should have pre-loaded DDF files but 3rd party devices may need to be loaded manually. To upload or verify the Modbus DDF, go to “Device > Modbus Device Communication Settings> Device Definition Files”. To upload or verify an SNMP DDF, go to “Device > SNMP Device Communication Settings> Device Definition Files”. If the correct DDF is not present please contact your local tech support. Tech support may be able to provide a DDF or, if a new DDF needs to be created for your specific device, they can get you in touch with a team that creates these files.

For DCE version 7.2.x and above, you can send devices to a specific group during discovery. Make sure to take note of which group you are adding the device.

If the device is not showing up after running the Discovery 
Try highlighting the “All devices” group and searching for the devices IP under the “Device View” tab to make sure it did not add under a different folder. You can usually either find the device by IP or hostname. 

Check the logs on the device to see if there are any unauthorized attempts to access the device. If there are unauthorized attempts listed the credentials being used(ex. SNMPv1 community strings or SNMPv3 User information) may be incorrect in your discovery. 

(CID:83656827)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:05 AM . Last Modified: ‎2024-04-10 01:47 AM

0 Likes
0
4744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:05 AM . Last Modified: ‎2024-04-10 01:47 AM

Can you please confirm that the Modbus TCP feature does not need extra licenses? Thanks.

(CID:96764323)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:05 AM . Last Modified: ‎2023-10-31 11:02 PM

0 Likes
0
4744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:05 AM . Last Modified: ‎2023-10-31 11:02 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore