Hello,
I have an issue with the detection of my device sensor, I can't get temperature value, power consumption of my snmp device . Even if I put the oid in the setting of snmp, struxuware don't give me more informations on my sensor
How can I resolve this problem ?
(CID:132650310)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 06:40 PM . Last Modified: ‎2024-04-04 11:28 PM
Hi Kemal,
Your first choice should always be to put in a DDF request. This is for new DDFs or for update to current DDFs and they should be able to assist in getting any of the values available through SNMP on your device.
If using supplemental OIDs, please make sure you try with a leading period. For instance, instead of:
1.3.6.1.4.1.318
use
.1.3.6.1.4.1.318
Notice the leading period.
Secondly, make sure you use the correct instance(s). As an example, the following OID is for an APC UPS and it's battery capacity:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsBattery.upsAdvBattery.upsAdvBatteryCapacity
.1.3.6.1.4.1.318.1.1.1.2.2.1
This will not return a value in DCE. You should do an SNMP get of the OID to see the proper and available instances and in this case, the device will respond with an instance of 0...you'll need to use the following OID to get this value:
.1.3.6.1.4.1.318.1.1.1.2.2.1.0
Another thing to consider is that there is no multiplier. If you pull an OID similar to the one I just mentioned, it may return the value in tenths. At 100% capacity, it may return 1000 to indicate 100.0%
Finally, a supplemental OID in DCE will only work with numeric values. Text will not work and if you were to even poll a value such as time (hh:mm:ss), you will not receive any values after the colon. you may simply see "hh" and nothing else. This is a limitation of supplemental OIDs.
Much of this should also be noted in k-base FA158341
If you're not getting any values at all, it could be that you need to troubleshoot SNMP as a whole. K-base FA226273 should help with that.
Thanks,
Steve.
(CID:132650325)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 06:40 PM . Last Modified: ‎2024-04-04 11:28 PM
Hi Kemal,
Your first choice should always be to put in a DDF request. This is for new DDFs or for update to current DDFs and they should be able to assist in getting any of the values available through SNMP on your device.
If using supplemental OIDs, please make sure you try with a leading period. For instance, instead of:
1.3.6.1.4.1.318
use
.1.3.6.1.4.1.318
Notice the leading period.
Secondly, make sure you use the correct instance(s). As an example, the following OID is for an APC UPS and it's battery capacity:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsBattery.upsAdvBattery.upsAdvBatteryCapacity
.1.3.6.1.4.1.318.1.1.1.2.2.1
This will not return a value in DCE. You should do an SNMP get of the OID to see the proper and available instances and in this case, the device will respond with an instance of 0...you'll need to use the following OID to get this value:
.1.3.6.1.4.1.318.1.1.1.2.2.1.0
Another thing to consider is that there is no multiplier. If you pull an OID similar to the one I just mentioned, it may return the value in tenths. At 100% capacity, it may return 1000 to indicate 100.0%
Finally, a supplemental OID in DCE will only work with numeric values. Text will not work and if you were to even poll a value such as time (hh:mm:ss), you will not receive any values after the colon. you may simply see "hh" and nothing else. This is a limitation of supplemental OIDs.
Much of this should also be noted in k-base FA158341
If you're not getting any values at all, it could be that you need to troubleshoot SNMP as a whole. K-base FA226273 should help with that.
Thanks,
Steve.
(CID:132650325)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 06:40 PM . Last Modified: ‎2024-04-04 11:28 PM
Hello Steve,
Thank you very much , I can clearly understand now.
(CID:132659396)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 06:40 PM . Last Modified: ‎2024-04-04 11:27 PM
Dear kemal,
Tell us please, did you solve your problem or not?
With respect.
(CID:132653782)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 06:40 PM . Last Modified: ‎2024-04-04 11:27 PM
yes the problem is solved
(CID:132653922)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 06:40 PM . Last Modified: ‎2024-04-04 11:27 PM
Ok, thanks for the good feedback 😀.
(CID:132653938)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 06:41 PM . Last Modified: ‎2023-10-22 02:18 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of