How To Model In Rack Rectifier

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How To Model In Rack Rectifier
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

0 Likes
4
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

How To Model In Rack Rectifier

What is the best way to model an in rack rectifier.  I have two similar situations

 

In both cases there is some DC powered kit in a rack, this is powered by an in rack rectifier.  One situation is the rectifier is connect to in rack AC power strips and the other is the rectifier is connected to an AC breaker.

(CID:113641154)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

0 Likes
2
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

If you want to show it in power path and have its load calculations taken into account, you can model the rectifier as an IT device that gets power from the rack pdu or off of a power panel.  

If you are trying to model the DC power path and the devices it powers, thats a different story.

 However as of right now, there are some limitation in what you can do with DC power path.  it follows all of the same rules as a floor UPS:

  1. it cannot have an AC source, it is the highest point in the power path
  2. it cannot be mounted in a rack, it has to be a floor device
  3. it cannot have DC distribution, you need to create a separate DC floor pdu
  4. it can't feed device directly, you have to have a DC pdu which then feeds DC rack pdus
  5. if it is dual fed, dual output for A/B sources, you need to make 2 devices, one for A feed, one for B feed.  This also applies to in rack dc fuse panels, you need to make 2 shelf mount devices that are half the size. 

 

(CID:113641300)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

In response to DCIM_Support
0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

Andrew Trabert - So at the moment DCO can't accurately model the situation, can this be caputred as a feature request?

Would you be able to advise what the best model is in DCO for the following;

 

Switch A is powered from Power Unit A & B.  Power Unit A is fed from the Orange in rack power strip and Power Unit B from the Grey.  The two in rack power strips are connect to a breaker on a power panel.

 

At the moment it is showing 4 power connections in the rack (giving it double the capacity)

 

Also there seems to be an error whereas there is 0kW capacity for each unit, even thought the power strips are connected

 

It's also not showing live readings, but I feel that is a seperate issue

 

(CID:113641529)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

In response to DCIM_Support
0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2024-04-08 01:37 AM

correct, its not a 1:1 representation, but it can still be modeled, albeit a little convoluted.

you can't model a rack pdu feeding a rack pdu or rack mount ATS ( DCO also does not support dual fed rack ATS').  You also can't power a device from a different rack.

Model Power unit A/B as generic rack mount equipment, then increase the outlet count in the zero U rack mount power strips so that they equal the number of outlets in both the rack mount power strip and the horizontal power strip -1.  Then connect Switch A to the zero U rack mount power strips.  

From a power path/capacity perspective, Daisy chaining rack pdus just adds outlets, not power capacity, so this work around still accounts for that.  The only thing it doesn't do is include the horizontal power strips in impact analysis. 

(CID:113641727)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2023-10-22 02:17 AM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:26 PM . Last Modified: ‎2023-10-22 02:17 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore