Hi,
For the following generic genomes I cannot add 2 pole circuit breakers. Please let me know if this is intended operation.
How do I model a panel with a 2 pole circuit feeding it with 2 pole circuits going out of the panel?
Thanks,
Chris
(CID:143760018)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:28 PM . Last Modified: 2024-04-03 02:38 AM
DCO has a simple way of looking at poles: 1/3 pole breakers supports 1/3 phase connections with the neutral (and ground) as implicit, that is, they are not modeled. 2 pole breakers supports a connection between 2 phases without a neutral (ground is still implicit).
Since all the equipment in your list are 1 phase, DCO wants to help you by removing the 2/3 pole/phase breakers from the list, that is, you cannot add a 2/3 pole breaker to a 1 phase panel because the other phases are missing in that equipment.
However, it is possible to create 1 pole breaker that takes up more space than one pole, here is how it is done:
When you use this new breaker you will see that it takes up 2 positions and thus looks like a 2 pole breaker.
BR
Gert
(CID:144311105)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:28 PM . Last Modified: 2024-04-03 02:38 AM
I was kind of thinking since the only options for panels seem to be 1P or 3P, that 1P == Single Phase. Thank you for clearing that up.
Is there a generic GEN_2P_ATS or GEN_2P_POWER_PANEL i can use? If not would that be a Genome request?
Thanks,
Chris
(CID:144312448)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:28 PM . Last Modified: 2024-04-03 02:38 AM
Sorry, but that is not possible because DCO does not have the ability to create 2P equipment.
That is, DCO does not support equipment connected to 2 phases and neutral, for equipment with phase-to-phase connections (no neutral) the 1P devices can (in most cases) do the job with the work-around I suggested in my first reply.
BR
Gert
(CID:144868438)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:28 PM . Last Modified: 2024-04-03 02:38 AM
Gert,
Thank you for the explanation. This is unfortunate since we have a site with several 2 pole UPS and panel boards.
-Chris
(CID:144868636)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:28 PM . Last Modified: 2023-10-22 02:07 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.