Galaxy 7000 ups not communicating with DCE 7.2.2

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Galaxy 7000 ups not communicating with DCE 7.2.2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

0 Likes
10
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

Galaxy 7000 ups not communicating with DCE 7.2.2

(CID:89063735)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

0 Likes
4
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

Yes. There is an issue in 7.2.2 DCE with Galaxy 7000 UPSes.

You have to ask APC to give you appropriate patch.

7.2.0 was Ok, not sure about 7.2.4.

(CID:89063737)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

0 Likes
4
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

Yes. There is an issue in 7.2.2 DCE with Galaxy 7000 UPSes.

You have to ask APC to give you appropriate patch.

7.2.0 was Ok, not sure about 7.2.4.

(CID:89063737)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

Is it firmware related?

(CID:89063740)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

It looks like it DDF related πŸ™‚

(CID:89063743)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:53 AM . Last Modified: β€Ž2024-04-10 01:38 AM

Nick, no. This is DCE version related. DCE 7.2.4 is ok.

(CID:89063748)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:38 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:38 AM

Roman, Good News about 7.2.4. Trying to resolve this issue (you know where) i compared DDF versions between 7.2.0 and 7.2.2 and found out that only MGE.ddf had newer version. That is what prompted the idea to try 7.2.0 πŸ™‚

(CID:89063754)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

0 Likes
1
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

I will run a test with DCE 7.2.4 and come back to this forum.

 

(CID:89063751)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

Hi Mudzimu, when commenting on an answer please use "add comment" instead of "your answer", that will help keep the thread in order. Thank you.

(CID:89064040)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

Hello,

 

This issue was resolved in DCE 7.2.4. The issue was only present on 7.2.2 for 3rd party devices. There is a patch that can be applied to fix the issue on 7.2.2. 

 

The link for the patch is below: 

https://schneider-electric.box.com/s/y649mwel9y6wd3zv4reu

 

 

Regards,

B

(CID:89063756)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2024-04-10 01:37 AM

Just to give some feedback. I have tested the Galaxy 7000 with DCE v7.2.4 and it works ok. The sensor reading issue has been resolved as Breda put it to this forum.

(CID:89063761)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2023-10-31 10:59 PM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 07:54 AM . Last Modified: β€Ž2023-10-31 10:59 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of