Firmware upgrade problem with netbotz750

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Firmware upgrade problem with netbotz750
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:03 AM

0 Likes
8
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:03 AM

Firmware upgrade problem with netbotz750

After I upgraded the firmware of netbotz750 from 5.0.9 to 5.1.0, I found that the web could not be accessed and was prompted with HTTP ERROR 503.

(CID:141266473)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:03 AM

0 Likes
6
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:03 AM

Hello shenwei,

 

After upgrading to 5.1.0 from 5.0.1 (I am not aware of any version 5.0.9) you must reset the appliance and manually reconfigure it as noted in the 5.1.0 release notes here:

https://sxwhelpcenter.ecostruxureit.com/download/attachments/96044657/990-6096B.pdf?version=1&modifi...

 

Thanks,

Steve.

(CID:141266607)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:03 AM

0 Likes
6
2136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:03 AM

Hello shenwei,

 

After upgrading to 5.1.0 from 5.0.1 (I am not aware of any version 5.0.9) you must reset the appliance and manually reconfigure it as noted in the 5.1.0 release notes here:

https://sxwhelpcenter.ecostruxureit.com/download/attachments/96044657/990-6096B.pdf?version=1&modifi...

 

Thanks,

Steve.

(CID:141266607)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

I can't  reset the appliance as manual because I can't open the web UI.Can it be reset via SSH,or is there any other way?

In fact, after the upgrade, I was able to access the web UI normally at first, but the superuser account could not log on the web UI, and the password was not correct. But I'm pretty sure I entered the correct username and password. But then I couldn't access the web UI anymore, and I'm not sure if it was locked because I tried too many times?

(CID:141266649)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

Hello shenwei,

Too many bad passwords should not cause the system to go totally off-line. Perhaps a reboot (physically disconnect power and reconnect) may help. You don't need to necessarily access the web page to input the command 

If you've done this and it has worked,  you will need to manually reconfigure the NetBotz appliance with a serial connection as you did the initial configuration.


Thanks,

Steve

 

(CID:141266658)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

It still doesn't work,I think this is because of a web service error

(CID:141266913)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

Hello shenwei,

Console in (serial) and after login, type Shift X (capital X) and enter and you should break out to the linux prompt

Then run

./netbotz_app/reset.sh

 

Close out and then again serial in and set up the IP again.

 

Steve

(CID:141267174)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:18 PM . Last Modified: ‎2024-04-03 03:02 AM

P.S.

If you forgot the root password, the manual has a physical reset for that:

https://sxwhelpcenter.ecostruxureit.com/download/attachments/96044657/990-5934B.pdf?version=1&modifi...

(CID:141267182)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:19 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:19 PM . Last Modified: ‎2024-04-03 03:02 AM

Thank you,it worked!

(CID:141267446)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:19 PM . Last Modified: ‎2023-10-22 02:05 AM

0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:19 PM . Last Modified: ‎2023-10-22 02:05 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore