Fail to integrate a Pelco IJP121 with DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Fail to integrate a Pelco IJP121 with DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

0 Likes
24
2263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

Fail to integrate a Pelco IJP121 with DCE

I'm need integrate some Pelco IJP121 in DCE.

First i integrate in a NB570 there i shared the cameras

Second in DCE detect NB570 and the cameras as device

But when i go to the surveillance tag, no cameras can configured, so can´t assign the license, and rest of configurations

(CID:122689944)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 24
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

0 Likes
22
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

Hi Miguel,

 

Is the image appearing properly in the NetBotz appliance?

What firmware is on the Camera?

What version of firmware (Botzware) is on the appliance?

What version of DCE are you using?

Is this a hardware server or VM?

If VM, what licenses are on it exactly?

K-base FA167042 is something you may want to look into so as to verify the camera and NetBotz are working properly together.

 

Steve

 

(CID:122689952)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

Is the image appearing properly in the NetBotz appliance? Yes

What firmware is on the Camera?

What version of firmware (Botzware) is on the appliance?

What version of DCE are you using? 7.4.1.5

Is this a hardware server or VM? VM

If VM, what licenses are on it exactly?  25 devices , 1 surveillance and 15 nodes surveillance base

(CID:122689974)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:53 PM . Last Modified: ‎2024-04-08 12:03 AM

Hi Miguel, Does DCE show any other cameras in surveillance already?


Steve

(CID:122689978)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

No, only have this DCE this NB570 and the cameras, now only one

(CID:122689989)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

Miguel,

Can you see the Pelco image properly in the NetBotz appliance?

Have you checked the k-base I suggested?

 

Steve

(CID:122689994)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

Yes i see fine in NB, I check the k.base but i don´t see anything than must be wrong

(CID:122690011)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

Hi Miguel,

 

On the Pelco camera, what compression is the Primary stream set to?

What compression is the secondary stream set to?

What are the resolutions for each?

You stated that "But when i go to the surveillance tag, no cameras can configured"

Do I understand correctly that there is no image at all in surveillance?

In the regular DCE device view, is the NetBotz appearing properly? All it's sensors? Is the camera listed there?

Is this communicating via HTTP or HTTPS all around (Pelco-bot-DCE)?

Do you have another Pelco camera? Another NetBotz camera?


Steve

 

 

(CID:122690456)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

On the Pelco camera, what compression is the Primary stream set to?

What compression is the secondary stream set to?

What are the resolutions for each?

You stated that "But when i go to the surveillance tag, no cameras can configured"

Do I understand correctly that there is no image at al ni surveillance?

nothing

In the regular DCE device view, is the NetBotz appearing properly? All it's sensors? Is the camera listed there?

yes

Is this communicating via HTTP or HTTPS all around (Pelco-bot-DCE)? HttP

Do you have another Pelco camera? Another NetBotz camera? No

(CID:122690518)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

Steven i answerd your questions but would you like make a webex, to see the DCE?

(CID:122690474)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

Hi Miguel,

 

Something like that is a definite possibility but you'll have to contact tech support for that level of assistance. I'll look into this and see if I can find anything else to look for.


Steve

(CID:122690481)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

I don't usually like to ask for logs over the forum as they're not private but they may be necessary to troubleshoot more in-depth. Again, contacting support will allow those logs to remain private. You can get the DCE logs from http:///capturelogs .  Potentially something could be seen there.

 

Steve

(CID:122690497)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:54 PM . Last Modified: ‎2024-04-08 12:02 AM

There are 24 Mb how can upload it?

 

(CID:122690559)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

If you have a box folder that yuo can share, I can take a look.

(CID:122690588)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

yes i have, how can share ?

 

(CID:122690595)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

By other way, if a connect whith dce portal the gadget of cameras an see the image, it's strange

(CID:122690614)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

To share a link, you can post to this page. If you need this to be discreet, please contact support as mentioned earlier.

 

(CID:122690616)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

Hi Miguel,

 

I can't see exactly what is causing this comm issue but I am seeing dozens of messages like this in the NBC log file:


Comm lost with bot [id = BDB0445; model = NBRK0570; type = NetBotz Rack Appliance; label = NetBotz Rack Monitor 570; host = device; mac = 00:C0:B7:DB:04:45; version = V4_6_1_20170620_1400]

A definite comm issue exists so checking firewalls would be your first thing to look into. If the VM host has a firewall, I suggest starting there.

Another log, the messages file, has thousands of communications issues with Modbus devices. This has been going on since February.

Since this is the free 5 node version and unactivated, I suggest spinning up a new VM of DCE. You're using 7.4.1 so maybe download 7.4.3 and start there too. Again, I see no specific reason in the logs for this failure but since there are so many errors on the system, perhaps that in itself is slowing the system down. Starting with a fresh system will also tell you if it is specific to this DCE install or something else like VM host, network, or NetBot issue.

On the NetBotz side of things, the only other suggestion I can make is to try and remove the appliance and re-add it using the "Post-Only Mode" feature. This tells the NetBotz device to post it's information to DCE rather than waiting for DCE to poll the appliance. This option can be found under tools-->advanced in the advanced view software.

Steve.

(CID:122690660)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

P.S.

I deleted the link in this thread so nobody else can download the logs going forward. unless they have the link

 

Steve

(CID:122690663)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

Miguel,

 

Please check one other thing. Can you check DNS settings on DCE. I forgot about this one, k-base FA158423 notes this could happen with bad or no DNS.


Steve

(CID:122693560)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

Steven, i make a new virtual machine with 7.4.3, and in nb i put "Post Only mode" and there are no fw in VM. But don't work

Who are the port then use DCE for surveillance?

(CID:122691203)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:55 PM . Last Modified: ‎2024-04-08 12:02 AM

Hi Miguel,

 

Ports are the standard HTTP or HTTPS ports unless you've changed them. Did you verify the DNS as suggested?

What do you mean by:

" there are no fw in VM"?

 

Steve

(CID:122691209)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:56 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:56 PM . Last Modified: ‎2024-04-08 12:02 AM

Yes i verify DNS are correct

There are no firewall in VM for DCE

(CID:122691216)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:56 PM . Last Modified: ‎2024-04-08 12:02 AM

In response to DCIM_Support
0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:56 PM . Last Modified: ‎2024-04-08 12:02 AM

Hi Miguel,

 

As noted ni the other post you put up earlier, try getting rid of the intermittent communications issues. As I noted in this post previously, I saw a fairly large number of communications issues between the appliance and DCE. To me this means there's too much traffic on the network or the NetBotz appliance is too busy. 


Steve

(CID:122693100)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:56 PM . Last Modified: ‎2023-10-22 02:04 AM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:56 PM . Last Modified: ‎2023-10-22 02:04 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore