EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 11:57 AM . Last Modified: β2024-04-10 12:02 AM
Hi, i have multiple APC Symmetra UPS communicating with DCE. I want tk export some of those values to enterprise server like statuses and current values of different modules using snmp protocol. Is it possible and how?
(CID:96043579)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 11:57 AM . Last Modified: β2024-04-10 12:02 AM
Hi Shaf Alam,
You can not monitor DCE using SNMP and gather device specific data. If you must use SNMP to gather this data, you must poll the devices directly. If SNMP is not a requirement, the DCE server can be configured to output Modbus over IP with the purchase of an AP95MODBUS license key and DCE would then be able to output data on up to 247 devices.
Steve
(CID:96043581)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 11:58 AM . Last Modified: β2023-10-31 10:58 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.