I have a DCE 7.2.7 where i need to integrate the Eltek Smartpack2 controller, already have the DDF installed.
I tried the SNMP v1 and v3 whitout any results.
As anyone done this before
(CID:148344427)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:56 PM . Last Modified: 2024-04-03 12:38 AM
Dear António Carvalho,
It seems to me that a similar topic Eltek Smartpack2 DDF can help you a lot. Please read Ara Orujyan answer on this:
...I tied to configure SNMP v3, and it works.
I don't know why this device have such specific configuration in part of SNMP V1 & V2, but with SNMP v3 it works perfect.
With respect.
P.S.: DCE-7.2.7 version is already quite outdated. It is better to upgrade it to the latest version of DCE-7.7.1. There are many changes and improvements in the new versions aimed at increasing the speed of the DCE-client and expanding its options.
(CID:148344490)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:56 PM . Last Modified: 2024-04-03 12:38 AM
Dear António Carvalho,
It seems to me that a similar topic Eltek Smartpack2 DDF can help you a lot. Please read Ara Orujyan answer on this:
...I tied to configure SNMP v3, and it works.
I don't know why this device have such specific configuration in part of SNMP V1 & V2, but with SNMP v3 it works perfect.
With respect.
P.S.: DCE-7.2.7 version is already quite outdated. It is better to upgrade it to the latest version of DCE-7.7.1. There are many changes and improvements in the new versions aimed at increasing the speed of the DCE-client and expanding its options.
(CID:148344490)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:56 PM . Last Modified: 2023-10-22 02:00 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of