Eltek Smartpack2 Integration
I have a DCE 7.2.7 where i need to integrate the Eltek Smartpack2 controller, already have the DDF installed.
I tried the SNMP v1 and v3 whitout any results.
As anyone done this before
(CID:148344427)
- Labels:
-
Data Center Expert
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:56 PM . Last Modified: 2024-04-03 12:38 AM
Dear António Carvalho,
It seems to me that a similar topic Eltek Smartpack2 DDF can help you a lot. Please read Ara Orujyan answer on this:
...I tied to configure SNMP v3, and it works.
I don't know why this device have such specific configuration in part of SNMP V1 & V2, but with SNMP v3 it works perfect.
With respect.
P.S.: DCE-7.2.7 version is already quite outdated. It is better to upgrade it to the latest version of DCE-7.7.1. There are many changes and improvements in the new versions aimed at increasing the speed of the DCE-client and expanding its options.
(CID:148344490)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:56 PM . Last Modified: 2024-04-03 12:38 AM
Dear António Carvalho,
It seems to me that a similar topic Eltek Smartpack2 DDF can help you a lot. Please read Ara Orujyan answer on this:
...I tied to configure SNMP v3, and it works.
I don't know why this device have such specific configuration in part of SNMP V1 & V2, but with SNMP v3 it works perfect.
With respect.
P.S.: DCE-7.2.7 version is already quite outdated. It is better to upgrade it to the latest version of DCE-7.7.1. There are many changes and improvements in the new versions aimed at increasing the speed of the DCE-client and expanding its options.
(CID:148344490)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:56 PM . Last Modified: 2023-10-22 02:00 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.