Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

EcoStruxure IT mobile app: no Daily push, no Alarm notifications, no Incidents are created for the last 6 days!

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forĀ 
ShowĀ Ā onlyĀ  | Search instead forĀ 
Did you mean:Ā 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • EcoStruxure IT mobile app: no Daily push, no Alarm notifications, no Incidents are created for the last 6 days!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

0 Likes
11
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

EcoStruxure IT mobile app: no Daily push, no Alarm notifications, no Incidents are created for the last 6 days!

Hi EcoStruxure IT support team,

1. For some unknown reason, EcoStruxure IT mobile app for Android (v. 1.0.50) has not receive a Daily push for the last 6 days, although the critical alarms for these days were:

2. In addition, when there is an alarms from devices not upgraded to Asset Advisor (not are Premium devices), there are no alarms notification. In my screenshot above, you can clearly see two critical alarms and you can not see any alarm notifications about this. I want to note that in the mobile app settings push notifications is not disabled:

3. The most important thing is that if there are alarms from devices upgraded to Asset Advisor (Premium devices), no incidents are created and there are no alarm notification!

All the above I checked on different smartphones under different accounts and for different gateway configurations (with SxW DCE-7.5.0 and with EcoStruxure IT GW-1.3.4.6).

I hope for quick help in solving this bug.

Very thanks for the support.

(CID:132664130)

Labels
  • Labels:
  • IT Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

0 Likes
9
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Hi

Can you please create a ticket Inside the app.

If you navigate to a device with an alarm, then in the top right corner of the screen, it“s possible to create a ticket, then we can find you in the system.

"alarms from devices not upgraded to Asset Advisor (not are Premium devices)" are no longer getting push notifications, in order to get notifications for those devices, they needs to be upgraded to premium.

Best Regards

Jacob

(CID:132664448)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Dear Jacob Just,

First, thanks for the answer.

1. The good news: I today again checked whether incidents are created for Premium upgraded devices. I can confirm that yes, incidents are successfully created. It is very good šŸ˜€.

The bad news is that I found a new bug in the latest EcoStruxure IT Android mobile app ā˜¹ļø.

The essence of the bug: Incidents incorrectly display the duration of the alarm.

For example, the alarm occurred at 13:49 (local time). Only after 8 minutes an incident was created for this alarm, i.e. at 13:57 (local time). At 14:05 (local time), the alarm was successfully closed, and after 2 minutes at 14:07 (local time) an incident was closed on this alarm.

Thus, the real duration of the alarm was only 16 minutes (from 13:49 to 14:05). But in the Android mobile app, we see an 1 hour, for example as on the explanatory screenshots:

I hope I have very clearly explained the essence of this bug.

2. Regarding Alarm notifications from not Premium upgraded devices: you answered on my question. But I and the DCIM community want, that about these and similar changes in the EcoStruxure IT digital service, somewhere notified. I think this is a good practice when working with end customers of digital services šŸ˜€.

3. And what about the Daily push? Or now the Daily push will be sent only in case of alarms from Premium upgraded devices during the last day?

4. And one more important question: I would like to receive Alarm notifications from different devices (as a rule it's native Schneider Electric rack ATS, rPDU, PDU and so on) as before. But if you look at the latest Android mobile app, you can see that they can not be Premium upgraded. I.e. in the list of these devices there is no "green crown", and the corresponding tab is gray, unlike devices that can be potentially Premium upgraded. This is clearly seen in the screenshot below:

How to solve this problem?

Very thanks for the support.

(CID:132664663)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Hi 

I“m happy to see push are working again. Thank you for the detailed information about the alarm duration bug, we are currently working on a solution for this.

You are right about the missing communication, we will be sure to do better next time we have breaking changes.

Regarding the daily push, it includes the total number of alarms, including alarms from devices without premium.

You should be able to upgrade all devices to premium, if you click on the grey crown, you will get into our premium upgrade system.

Best Regards

Jacob Just

 

(CID:132670672)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:08 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Dear Jacob Just,

From your comments:

...Thank you for the detailed information about the alarm duration bug, we are currently working on a solution for this.

You are right about the missing communication, we will be sure to do better next time we have breaking changes.

That is, in the new version of EcoStruxure IT mobile app 1.0.51 (from July 30, 2018), these problems have not been resolved yet? Unfortunately, in the above-mentioned new version of the mobile app, there is also no brief information about the changes/fixes made ā˜¹ļø.

Regarding the daily push, it includes the total number of alarms, including alarms from devices without premium.

I want to clarify: if during the day there were alarms only from non premium devices (there were no incidents), then the daily push will not work? For example, I now have several alarms every day from non premium devices, but daily push does not work as it was before. Explain please this situation.

You should be able to upgrade all devices to premium, if you click on the grey crown, you will get into our premium upgrade system.

Yes, of course I already know about this, so my previous question number 4 is almost solved. Almost, because according to the information on the official website https://ecostruxureit.com/ecostruxure-asset-advisor/:

How do I subscribe to Asset Advisor?

Before you can subscribe to Asset Advisor you need to have the EcoStruxure IT Gateway and app. Sign up to get the mobile app here.

Log into app.ecostruxureit.com/manage to subscribe assets to Asset Advisor.

 

Note: Assets covered by Advantage Prime, Advantage Ultra, Factory Warranty, Onsite Warranty Extension, and Fleet Management contract will not be charged upon subscription to EcoStruxure Asset Advisor. Does not apply to India.

That is, I have exactly this situation, as indicated in the notes on the website. For example, my Symmetra PX 500 in a mobile app is displayed with a white-green crown, that is, potentially this UPS can be upgraded to a premium without paying any money. But as soon as I try to do this, they tell me that it is necessary to pay money. Why?

On this occasion, on July 16, 2018, I created the incident 8846344, where I indicated the my Service contract number for the Symmetra PX 500 UPS. But unfortunately the incident was not taken to work (Assigned to: None) and is now in the open state. Explain please this situation.

Very thanks for the support.

(CID:132670733)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

HI 

We are only sending the daily push, when the gateway had alarms/incidents during the last 24 hours. 

What country are you from, it seems like you are in a country not supported yet, we have not released world wide yet, please refer to this link: https://ecostruxureit.com/available-in/

Best Regards

Jacob Just

(CID:132670741)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Dear Jacob Just,

We are only sending the daily push, when the gateway had alarms/incidents during the last 24 hours.

We have this situation, but the daily push does not work...

What country are you from, it seems like you are in a country not supported yet, we have not released world wide yet, please refer to this link: https://ecostruxureit.com/available-in/

Yes, of course I am aware of this. The unpleasant news is that, more recently, the basic functionality of the digital service EcoStruxure IT has become simply not available for unsupported countries ā˜¹ļø. This is a step back from Schneider Electric, as you had good opportunities for final debugging above the specified service. I hope, that this situation will change in the near future.

With respect.

(CID:132670758)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Hi

I understand the situation, I will look at the daily push, it should work. Once released this product might fit your needs perfect: https://ecostruxureit.com/ecostruxure-it-expert/ 

Best Regards

Jacob Just

(CID:132670760)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Hi

 

A short update, I have checked our daily push service, and it“s working correctly. Since you are in a unsupported country, we have not tested our system there, so services like push notifications might not be stable.

 

Best Regards

Jacob Just

(CID:132671307)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Ok, anyway, thanks for the support.

(CID:132671309)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

In response to DCIM_Support
0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2024-04-04 04:18 AM

Dear Jacob Just,

It seems that in the version 1.0.59 of the mobile app daily push again work.

Good job šŸ˜€.

(CID:134024353)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2023-10-22 02:00 AM

0 Likes
0
1999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:09 PM . Last Modified: ā€Ž2023-10-22 02:00 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Ā© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore