Posted: 2022-09-2602:39 PM
EMCP 4 generator integration
Hello! Could you help me, I integrated an EMCP 4 generator to the DCE but when the equipment is alarmed the notifications do not arrive and the DCE does not appear alarmed.
2)If there are predefined alarms, what is the polling interval for the device? you can check this in Device -->snmp/modbus device comm settings --> device scan settings. Edit the device and lower the polling interval to 1 or 2 mins. This way when an alarm occurs, DCE will see it in a min or 2
3) if the above is true and you still missed an alarm, it's possible it wasn't active for longer than 1 min. This is unlikely with a generator, but possible.