Dry Contacts from NB250 not showing on device in DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Dry Contacts from NB250 not showing on device in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

0 Likes
9
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

Dry Contacts from NB250 not showing on device in DCE

Hi All,

I have a strange occurrence of getting a NB250 dry contacts to register as device inputs within data centre expert!  DCE version 7.4.2 and NB250 firmware is 6.4.5.

I have requested device scans to reload the inputs from the NB250, however this doesn't collect these inputs.  We need to get this one working as we alert and monitor centrally not from end nodes, as they SNMP trap there alerts.

 

Any help appreciated.

(CID:110794364)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

0 Likes
2
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

HI Matthew,

 

Good morning.

I duplicated your issue and found out same result.

I also contacted software team and it was indeed a DDF concern as advised by Bala on his reply.

Let's wait for the next DDF update and this should be resolved.

 

Best regards,

Jezreel

(CID:110795136)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

0 Likes
3
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

Hi Matthew,

1.Discover the netbotz 250 as SNMP device in DCE

2.Contact tech support with your DCE's software support contract to get upgrade for your DCE.

(CID:110794372)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

In response to DCIM_Support
0 Likes
0
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

Hi Chrisopherous,

Sorry DCE is actually version 7.4.2 the current release.  Also sadly I avoid our local APAC Support as shifted to Manila, away from a Sydney contract, the support there has yet to pickup in the correct way.  Hence I have found much more useful information from using DCIM forum, and also getting additional support from other users, and Schneider Support.

 

Thanks for your suggestions.

 

Matthew

(CID:110794379)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

In response to DCIM_Support
0 Likes
0
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

Hi Matthew,

Let us know how things are going with your netbotz 250.

Sorry to hear your experience. Do drop me note separately with your feedback on support & your contract. Will pass it to relevant party to follow up with you.

 

Chris

(CID:110794395)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

In response to DCIM_Support
0 Likes
0
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:30 PM . Last Modified: ‎2024-04-08 01:55 AM

Hi Chris,

Thanks for that, and still no more update from APAC support.

Waiting this long for a APC DDF file for a APC product is not acceptable, for what we pay for support.

 

 

Cheers,

 

Matthew

(CID:111415947)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

0 Likes
0
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

Dear Matthew,

If possible, please upload the recent attached NBRK0250 DDF in DCE software and see if your issue gets fixed. 

netbotz250.zip

To import the attached DDF file:

Main menu->Device->SNMP Device Communication Settings->Device Definition Files->Add/Update Definitions

If you still see the issue, then please raise your request with DDF team here.

I hope this helps. 

Regards,

Bala

(CID:110794392)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

0 Likes
2
1446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

HI Matthew,

 

Good morning.

I duplicated your issue and found out same result.

I also contacted software team and it was indeed a DDF concern as advised by Bala on his reply.

Let's wait for the next DDF update and this should be resolved.

 

Best regards,

Jezreel

(CID:110795136)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

In response to DCIM_Support
0 Likes
0
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

Thank You Jazreel

We are looking forward to a DDF file update, strange that this was missed on testing prior to the NB250 release.

Will the DDF file be available for download directly from the DDF update server?

 

Matthew

(CID:110795140)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

In response to DCIM_Support
0 Likes
0
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2024-04-08 01:55 AM

Hi Matthew,

 

Yes, as long as they're available. we can update the DDF from "add/update Definitions".

Rest assured that you'll also be notified immediately.

 

Regards,

Jezreel

(CID:110795162)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2023-10-22 01:56 AM

0 Likes
0
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:31 PM . Last Modified: ‎2023-10-22 01:56 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore