Does Third party PDUs (Single IP with multiple sensors) can be associate with DCO basic rack pdus?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Does Third party PDUs (Single IP with multiple sensors) can be associate with DCO basic rack pdus?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
8
830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

Does Third party PDUs (Single IP with multiple sensors) can be associate with DCO basic rack pdus?

Hi

Please clarrify 3rd party PDU / Line meters which have single ip connected with multiple Basic rack PDUs. How to associate the Power and Temperature sensors in DCO basic pdus?

The example products are mentioned below:

Chatworts Product (CPI) – Diasy Chain Connection upto 20 PDUs in a single IP 

- Panduit- Unite CL Amp – where I can use Eagle-I (having single IP) with multiple Clamp Meters or PDUs or sensors

RacKMS - Single IP with multiple Clamp meters for Basic PDU measurement.

(CID:89064339)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

Hi Venkat,

An option that has worked for us with Unite / Eagle-i is to create a virtual sensor in DC Expert for each active power point.

Associate that virtual sensor to the Rack PDU upstream distribution PDU, then use branch circuit mapping to map the virtual sensor to the circuit outlet that corresponds to the Rack PDU.

This if for DCO 7.4, not sure if this works in prior versions

(CID:90243188)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

Hi Venkat,

You will get as many sensors you have in DC Expert for the discovered devices. Please share the snaps from DCE & DCO- Device Associations. If you are able to see the sensors & all their sub-sensors in device association, only then you will be able to associate them.

(CID:89064349)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

Thanks Aniruddh,

I didn't see the sensors & all their sub-sensors in DCO device association for this product. Please find herewith the RacKMS and DCE Snapshots for your reference.

Is there any work around / road map to add these kind of products single IP with multiple sensors for Basic Rackpdu DCO association?

 

(CID:89064375)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:15 AM . Last Modified: ‎2024-04-10 01:34 AM

Hi Venkat,

As per your observations, you see common sensors discovered in DCO for power & environment so you cannot have them segregated & mapped against the actual physical location of the device. To achieve this you need to have them discovered separately. Well, here we are solely dependent on the way the third party devices make the data available to DCO after their discovery. You can map the only device discovered in DCO & let it report all the data. Thanks. 

(CID:89064425)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

0 Likes
2
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

Hi Venkat,

Specific case = custom solution 😀 

Take a look at our ETL integration possibilities. I have solved recently a similar problem by building a custom integration between DCE and DCO, pushing to DCO the different sensors independently (each power sensor = one device), so you can associate them to the rackPDU you want to. We end-up with a very similar behaviour than the standard integration DCE/DCO: peak and average values, KPIs generation...etc

(CID:89555647)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

In response to DCIM_Support
0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

Hi Vigneron, can you compile the same into a information presentation with snapshots showcasing the way you did it so that we can work on similar patterns as well. I believe when you say pushing each power sensor as one device , did you modify the MIB and DDF to report the parameters in such way?

(CID:89556790)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

In response to DCIM_Support
0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

Hi Vineet, I did not modify the way DCE recognise the devices and sensors, so I didn't touch to MIB and/or DDF. I created an ETL integration that request to DCE (via web-services) the list of the concerned devices, based on the result I request then the list and values of the sensors in these devices. I pushed the information to DCO in the following form: each sensor is a device with one power measurement. The end result in DCO is a list of devices (each one representing one power measurement) that I can associate one by one to my modelled rackPDUs. This require knowledge on DCE web-services and ETL and must not be considered as a plug and play solution. It's a professional service that require some time for: -understanding the exact situation -developing the ETL process -deeply testing the solution We can help you guys if you face that sort of situation, feel free to contact us.

(CID:89556799)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

0 Likes
0
830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2024-04-10 01:33 AM

Hi Venkat,

An option that has worked for us with Unite / Eagle-i is to create a virtual sensor in DC Expert for each active power point.

Associate that virtual sensor to the Rack PDU upstream distribution PDU, then use branch circuit mapping to map the virtual sensor to the circuit outlet that corresponds to the Rack PDU.

This if for DCO 7.4, not sure if this works in prior versions

(CID:90243188)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2023-10-31 10:55 PM

0 Likes
0
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:16 AM . Last Modified: ‎2023-10-31 10:55 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of