PDPM138H-5U doesn,t have breaker option

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • PDPM138H-5U doesn,t have breaker option
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
5
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

PDPM138H-5U doesn,t have breaker option

We are facing one issue in DCO, Customer is having PDPM138H-5U (APC rack mounted distribution panel) fitted in one of the rack, where it supplies the power to the rack pdu installed in same rack as well as other rack pdu in different rack. When we add this device as per its model name from gnome we could see that it has only power option but cannot add breaker in it. Due to this issue we could no power other device from it.Please suggest 

the solution as customer doesn't want any temporary solution. 

(CID:89064143)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

There is no solution for it as PDPM has to provide breaker option than only other devices physically connected to it can be resolved. 

(CID:89064145)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
1
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

Hi Atul,

There is a question and answer already in the community 

Currently, modeling 5U RDPs in StruxureWare Data Center Operation is not supported. You can get around this by following the below workaround.

Workaround:

  1. Use PDPM138H-5U or create a customized 5U RDP from a generic component in Genomes.
  2. Add the 5U RDP to a rack to indicate that the U-space is occupied.
  3. Create a fake floor-mount power panel in Genomes in the same way as the RDP.
    Make sure you configure the power distribution attributes.
  4. Place the power panel in the floor layout, for example just behind the rack in which it is positioned in the real data center.
  5. Connect the fake power panel to the rack PDUs to model the power path.

 

Note: The fake object will be visible in the 3D view and inventory report.

 

(CID:89064173)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

In response to DCIM_Support
0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

As a curiosity the PDPM138H-5U thinks (in DCO model terms) that it is a rack mount PDU with only one power outlet ...

(CID:89064309)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2024-04-10 01:34 AM

Dear Atul,

This is a notified finding. Presently PDPM138H can only be modeled but cannot provide any further power distribution. 

(CID:89064171)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2023-10-31 11:28 PM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:14 AM . Last Modified: ‎2023-10-31 11:28 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore