Do firmware updates require reboots?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Do firmware updates require reboots?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:34 AM . Last Modified: ‎2024-04-08 11:18 PM

0 Likes
8
6127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:34 AM . Last Modified: ‎2024-04-08 11:18 PM

Do firmware updates require reboots?

Hi,

I am planning to update all our UPS, PDUs, and Netbotz from Data Center Expert. Will updating the firmware require downtime on all the units? Or will the web cards reboot unobtrusively without bringing the units down, so we'll get communication outages but not require a maintenance window?

Thanks.

(CID:108235164)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

In response to DCIM_Support
0 Likes
0
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

Hi Muhammad Touseef - Rack ATS has a special firmware upgrade procedure you must follow. See this link-> http://www.apc.com/us/en/faqs/FA156178 . If you do not follow it, you could have problems and cause damage to the ATS and if that happens, the load could reboot or worst case turn off. Upon applying a firmware update to ATS through DCE, you should receive a warning to do the stuff explained in the link above and outside of DCE, the firmware upgrade utility also warns about the upgrade process. So, if all process is followed - NO, load will not reboot or turn off during a Rack ATS firmware upgrade. As a side note, resetting to defaults/resetting ATS controller command action may cause a reboot as explained here -> http://www.apc.com/us/en/faqs/FA156352

(CID:108825544)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:34 AM . Last Modified: ‎2024-04-08 11:18 PM

0 Likes
6
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:34 AM . Last Modified: ‎2024-04-08 11:18 PM

Hi Dominic,

Yes, in the case of UPS and PDU, only the management interfaces (the UPS or PDU Network Management Cards (NMCs) ) reboot for a tiny window of management downtime - output power to your connected loads will not be lost. I would urge you to just double check on any Rack PDUs that you do not have any active alarms though. There are a few very rare scenarios on switched rack PDUs (those strips with switched/controllable outlets) that if there is a problem with the management interface and it cannot reboot properly, the outlets won't re-energize and come back on. This is only in the case if you have internal lost communication failure alarms which would show through DCE or the device's web interface. If you have no active alarms revolving around what i mentioned, this will not be a worry. 

With NetBotz products, the entire appliance will reboot so you'll miss around 2-3 minutes of environmental monitoring during the upgrade.

Let us know if you have any other questions.

(CID:108235184)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:34 AM . Last Modified: ‎2024-04-08 11:18 PM

In response to DCIM_Support
0 Likes
0
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:34 AM . Last Modified: ‎2024-04-08 11:18 PM

Angela,

Thanks for the reply. Regarding rack PDUs, your statement that "the outlets won't re-energize and come back on" indicates that at some point during a normal update, the outlets usually turn off and on again, and the problem you reference stops that process. If that's the case then any equipment connected to them is going to go down regardless. Please clarify, as I thought that power to connected equipment should stay on during an update.

If I've understood the rest of your post correctly, you're saying that as long as DCE isn't showing any active alarms at the time of the update, we should be fine to update without requiring downtime on any of the equipment (other than the Netbotz). Is that correct?

Thanks.

(CID:108824314)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

In response to DCIM_Support
0 Likes
0
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

Hi Dominic, To clarify, for any type of Rack PDU during a normal update, the outlets do not turn on/off and they remain energized and in their current state when the NMC does the soft restart to load the new firmware. It is only in these edge cases I've seen where internal communication between NMC and switched Rack relay boards are not able to maintain the state of the relays, especially if the entire rack PDU is removed from input power and then powered up again. All of these scenarios are prefaced by an active alarm though so it is why I brought up, even though it is not a common occurrence. I am sorry for the confusion and unnecessary worry. Your last paragraph is correct. For any devices, including Rack PDU, as long as they are operating normally and you have no active alarms we should check prior, a firmware upgrade of the management interface done through any method, including DCE, will not power on/off any attached loads. Devices that require special upgrade processes (or that require field service) we don't provide firmware through DCE also to prevent or avoid any required downtime during any updates. Please let me know if you have any other questions.

(CID:108824317)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

In response to DCIM_Support
0 Likes
0
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

Thanks Angela. Can you give me a rough idea of how long PDU and UPS updates take? I'm trying to plan out a schedule and need to know how much of the maintenance window the updates will take. Thanks.

(CID:108824316)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

In response to DCIM_Support
0 Likes
0
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

Hi Dominic - APC Rack PDUs and the UPS Network Management Cards (the NIC for the UPS) take typically about 5-6 minutes to complete the upgrade process. This involves transferring 2-3 firmware files and a reboot in between each one. Depending on the generation/model of the PDU or NMC, it may go closer to 4-5 minutes and the older generation products, you may see closer to the 6 minutes per each device. NetBotz Rack or Wall appliances usually take around 5 minutes in my experience to transfer the file and then reboot and apply it.

(CID:108824315)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

In response to DCIM_Support
0 Likes
0
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

Hi Angela, What about Rack ATS.... do these devices reboot & turns off load following a firmware upgrade. Thanks,

(CID:108825529)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

In response to DCIM_Support
0 Likes
0
6120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2024-04-08 11:17 PM

Hi Muhammad Touseef - Rack ATS has a special firmware upgrade procedure you must follow. See this link-> http://www.apc.com/us/en/faqs/FA156178 . If you do not follow it, you could have problems and cause damage to the ATS and if that happens, the load could reboot or worst case turn off. Upon applying a firmware update to ATS through DCE, you should receive a warning to do the stuff explained in the link above and outside of DCE, the firmware upgrade utility also warns about the upgrade process. So, if all process is followed - NO, load will not reboot or turn off during a Rack ATS firmware upgrade. As a side note, resetting to defaults/resetting ATS controller command action may cause a reboot as explained here -> http://www.apc.com/us/en/faqs/FA156352

(CID:108825544)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2023-10-31 10:55 PM

0 Likes
0
6119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:35 AM . Last Modified: ‎2023-10-31 10:55 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore