Devices alarms in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Devices alarms in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
63
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:29 PM . Last Modified: ‎2024-04-03 03:20 AM

0 Likes
5
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:29 PM . Last Modified: ‎2024-04-03 03:20 AM

Devices alarms in DCE

Greetings!
I'm having an issue with alarm notifications in DCE. Netbotz appliances show correct thresholds and notifications in DCE, but PDUs, UPS, AA and power meters (not all are APC products) don't. Notifications via mail from the devices work fine, but DCE never notices about such alarms.
Question is: it has to be automatic or I must set up the configuration of appliances alarms on DCE. In such case, how can i do it?
My DCE version is 7.6.0 for Windows 10 64bitsThanks!

(CID:140708462)

Labels
  • Labels:
  • Data Center Expert
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:29 PM . Last Modified: ‎2024-04-03 03:20 AM

0 Likes
3
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:29 PM . Last Modified: ‎2024-04-03 03:20 AM

Hi Javier,

Are these all APC devices? If so, they should all alert based on the alarms listed under Alarm  Configuration, Device Alarm Configurations tab. This page shows all the alarms DCE is capable of showing and e-mailing for the devices.

If an APC device does not have these listed, there may have been errors about an FTP transfer. If they are listed, DCE should see them. This FAQ describes that potential issue:

http://www.apc.com/us/en/faqs/index?page=content&id=FA177004

 

The APC device should be seen as being in alarm almost immediately. If not, you may not have priority scanning set up. This k-base describes that feature:

http://www.apc.com/us/en/faqs/index?page=content&id=FA271584

 

3rd party device must wait until they are polled to show alarms and in most cases, thresholds must be manually created for those devices. If you have to create thresholds, this FAQ may halp:

http://www.apc.com/us/en/faqs/index?page=content&id=FA299560

 

If the alarms are showing within DCE but are not being sent, please note that NetBotz 3xx, 4xx, and 5xx devices send their own e-mails. DCE will send e-mails for any other alarm and that configuration can be found here:

http://www.apc.com/us/en/faqs/index?page=content&id=FA225766

 

If you need more help, please try to be a little more specific on what you're seeing, what you're not seeing, and what it is exactly that you are expecting.

Thanks,

Steve

(CID:140708468)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:29 PM . Last Modified: ‎2024-04-03 03:20 AM

In response to DCIM_Support
0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:29 PM . Last Modified: ‎2024-04-03 03:20 AM

So complete! Thank you!
Well, some of the devices are APC and some others not.
With the 3rd party ones, thresholds are already setted in the device interface, but it doesn't show in DCE.

Question: the alarms on the "Device alarm configuration" section are the alarms that i have the possibility of configure or the ones that ARE configured by default in DCE?

(CID:140708478)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:30 PM . Last Modified: ‎2024-04-03 03:20 AM

In response to DCIM_Support
0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:30 PM . Last Modified: ‎2024-04-03 03:20 AM

For example: The AA has 2 compressors and is working without one of them right now. DCE doesn't notify me about the fault of such compressor.

(CID:140708482)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:30 PM . Last Modified: ‎2024-04-03 03:20 AM

In response to DCIM_Support
0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:30 PM . Last Modified: ‎2024-04-03 03:20 AM

Hi Javier,

Under Alarm Configuration, you have 2 tabs... Device Alarm Configurations and Threshold Alarm Configurations. Any threshold that is set on the device itself must also  be present on the Device Alarm Configurations tab for DCE to show in it's alarms and to notify (e-mail) you about that alarm.

I wasn't sure if DCE was not seeing these alarms at all or just wasn't notifying you if it saw them, this is why I tried to be as complete as possible with my response. If a device is in alarm and you either wait the polling time or right click the device and scan now. If the alarm does not show up in the alarms tab or doesn't show a red 'X' or yellow '!', DCE won't e-mail you even if that part is set up correctly. I'll assume for now that this is the case, DCE doesn't even show an alert status. 

If the alarm you're looking for is on the list on the right hand side and the device is in alarm, DCE should see it. APC devices pull these alerts from a DDF on the device (essential alerts DDF) while 3rd party devices, if device alarms exist, have these threshold built into the scanner DDFs...you know, the ones you can request on this site. If the alarm is not listed on a 3rd party device, that DDF may need to be updated. The first thing I would suggest is to make sure DCE is up to date. I don't recall seeing a version number.

There also may not be a DDF with those alerts available in which case, you may need to create the thresholds manually. You can then add a device (and all it's device alarms) into an e-mail policy or you can add the individual manually created thresholds into those policies.

 

If the alarm is in the device alarms list on the right when selecting the device, if you've waited the poll cycle or requested a device scan, if the thresholds are enabled, yes, you can double click a threshold and disable it, then it's possible there is a DDF issue, conflict, or potentially what DCE is looking for in the device's SNMP stack is not there. At that point you'd need more specific device info, DDF info, packet captures of the device (or a similar one) both in and out of this alarm to really troubleshoot it well. You may want to contact support directly as that can get quite involved and doing these things over a forum can take time.

 

Steve

 

(CID:140708696)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:30 PM . Last Modified: ‎2023-10-22 01:54 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:30 PM . Last Modified: ‎2023-10-22 01:54 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of