Device Alarm Configuration

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Device Alarm Configuration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

0 Likes
12
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Device Alarm Configuration

Im trying to add the water detection device alarm to a notification policy that has already been created.

If i select the device group, i can see that under the Threshold Alarm Configuration tab that the communication status threshold has been added to the notification policy.

Under the Device alarm Configuration tab I can filter "Water" to show both Water Detection Fault and Water Detection Shut down alarms.

How do i add these alarm configurations to the policy?

(CID:134031068)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

0 Likes
9
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Dear Andrew Stoakes,

I assume that you mean NetBotz-200 or NetBotz-250 devices (not NetBotz-4.x appliance).

In this case, you just need to make sure, that in your Notification Policy name the device you need is added, for example as in the screenshot:

If you have any further questions, please ask.

With respect.

(CID:134031347)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

To add to what spezialist is saying, the manually created thresholds can be added individually but device alarms can not. To get device alarms to work with a policy, the entire device needs to be added to that policy using the procedure he's noted.

 

Steve

(CID:134031488)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:28 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Should have explained. This is with an Inrow cooler not a netbots device

We had a small leak on an InRow cooler that triggered an alarm in DCE but we had no notification.

Water detection faults are available under the Device Alarm configuration tab nut not configured in the Threshold Alarm configuration tab.

The question is, How do I make use of what appear to be pre-configured events.

(CID:134031799)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Dear Andrew Stoakes,

From your comments:

We had a small leak on an InRow cooler that triggered an alarm in DCE but we had no notification.

If briefly, please show a screenshot where it is clearly visible what Severity is set for Water Detection device alarms? And besides, what Notification Policy name set for Water Detection device alarms? That is, do as I have on the screenshot:

Then go to this Notification Policy name and see what Actions are there (see my screenshot Edit Notification Policy above)?

Then mark the required Action, click Edit... button and again click Manage Actions... Select the appropriate Action, click Edit... button and make sure that necessary Severity checkbox is marked, which is set for your Water Detection device alarms:

I hope this helps you.

With respect.

(CID:134031878)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

communication thresholds.

Thanks fro the reply. I have been through this but don't understand how to associate the Device alarm configuration with a notification profile. Some of the Water Faults are associated with a policy but others are not and i cant work out how or why some are and some are not or how to associate them with a policy. All severity's are associated with the policy that we have configured but i am unable to add anything to the policy. If i crate a new notification policy the only thresholds i have available are the communication thresholds.

(CID:134032281)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

 

It appears to be a bug. If i remove the device that has no policy and add it back in then I can add it to the policy. Still not showing up in the threshold section.

 

 

(CID:134032343)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Dear Andrew Stoakes,

From your comments:

...If i crate a new notification policy the only thresholds i have available are the communication thresholds.

This is as it should be. Since Threshold Alarms β€“ are customer alarms, you have to create them yourself. The only customer alarm that is created automatically is Communication Status.

With respect.

(CID:134032310)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Dear Andrew Stoakes,

This of course is not a bug πŸ˜€. What version do you have DCE software?

When adding a new device to the DCE software, for its Device Alarms (not Threshold Alarms), the notification policy is not applied (No Policy).

Therefore, once you have added a new device, you must right-click on the device and select Change Device Alarms Notification... -> change from No Policy to your required policy. Only after that all Device Alarms of your new device will have the required notification policy.

Try it.

With respect.

(CID:134032341)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Version is 7.5.0. My point was that for devices that already existed i could not add the policy to the device or device group. After right clicking and adding the policy it would not apply. 

After I removed the device(s) and added them back i could apply the policy...So that of course is a bug.

(CID:134032458)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

In response to DCIM_Support
0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Dear Andrew Stoakes,

From your comment:

...After right clicking and adding the policy it would not apply.

 

I use exactly the same DCE software, but I do not have such problems, i.e. I can not reproduce your bug πŸ˜€.

In your case, try to reboot your DCE-server. Tell us please, what is the uptime of your DCE-server (see web-link http://_DCE_Address_/nbc/status/Status)?

Important: do you make regular backups of your DCE-server?

With respect.

(CID:134032583)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:29 PM . Last Modified: β€Ž2024-04-04 02:32 AM

Dear Andrew Stoakes,

Tell us, please, did you solve your question or not?

With respect.

(CID:134680010)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 11:30 PM . Last Modified: β€Ž2023-10-22 01:52 AM

0 Likes
0
1257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 11:30 PM . Last Modified: β€Ž2023-10-22 01:52 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of