EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:45 PM . Last Modified: 2024-04-05 04:49 AM
Hi
is there any way to insert a power limitation to a room?
Example.
i have 4 room and my power is 100kW.
I'd like to set power for
Thanks
(CID:125211127)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:45 PM . Last Modified: 2024-04-05 04:49 AM
Set the input breaker rating at the PDU for the room, with breaker derating.
Set breaker derating at the main PDU output (before racks).
Set design limit on racks within the room
(CID:125211441)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:45 PM . Last Modified: 2023-10-22 01:51 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.