Datacenters and Netbotz

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Datacenters and Netbotz
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

0 Likes
4
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

Datacenters and Netbotz

Hi,

I have 3 datacenters (they are all interconnected) and I want to monitor them all. Do I need to buy 3 netbotz? Or Can I have 1 primary netbotz and 2 secondary? Can I use one netbotz appliance and 2  NetBotz Rack Sensor Pod 150? Can I connect them throught a switch? What is the best deployment for this case?

Thanks in advance for your help.

Have a nice day

(CID:125211138)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

Hi Sylvestre,

 

The NetBotz 150 pod connects to the NetBotz appliance using a cat-5 cable however it does not communicate over Ethernet. The pod has no IP address.  It communicates using a proprietary protocol called A-link based on the can bus topology. Although the pods can be set up a good distance away, it won't communicate over the network or through a switch. If the data-centers are in different cities for instance, you'll need to by each site it's own NetBotz appliance.

 

The distance A-link will work is up to 100 meters per length (from one pod/sensor to the next) up to a total of 1000 meters as per k-base FA156085.  

 

Thanks,

Steve

(CID:125211151)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

0 Likes
0
1257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

Hi Sylvestre,

 

The NetBotz 150 pod connects to the NetBotz appliance using a cat-5 cable however it does not communicate over Ethernet. The pod has no IP address.  It communicates using a proprietary protocol called A-link based on the can bus topology. Although the pods can be set up a good distance away, it won't communicate over the network or through a switch. If the data-centers are in different cities for instance, you'll need to by each site it's own NetBotz appliance.

 

The distance A-link will work is up to 100 meters per length (from one pod/sensor to the next) up to a total of 1000 meters as per k-base FA156085.  

 

Thanks,

Steve

(CID:125211151)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

Hi Sylvestre BELKOULAYO MBAYHAMNODJI,

I have 3 datacenters (they are all interconnected) and I want to monitor them all. Do I need to buy 3 netbotz?

Steven Marchetti correctly noted that the limiting factor for you can be the length of the communication line and its type (this should be a copper communication line, not optical). This is the first.

Secondly, it is very important what kind of devices you are going to monitor, how many of them. In addition, it is very important to know whether you will use video surveillance cameras and what their number will be.

Or Can I have 1 primary netbotz and 2 secondary? Can I use one netbotz appliance and 2  NetBotz Rack Sensor Pod 150?

Perhaps, for you it will be possible to do (for example, a small distance between datacenters, a small number of monitoring devices and surveillance cameras, very limited budget, etc.). But think about the reliability of this monitoring system: the monitoring system will depend on the reliability and quality of communication lines and the reliability of only one datacenter, in which the NetBotz main module will be located. And if the connection with only one this data center is interrupted, you will lose monitoring at once all of your datacenters and will not even receive any notification of this incident (because only the NetBotz main module sends notifications).

Therefore, your question is not as simple as it seems, and requires a more detailed examination of your requirements and wishes for the monitoring system of the three datacenters.

Always glad to answer your questions.

(CID:125211308)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM

Hi Steven, Hi Spezialist

Thanks for your answer.

 

Have a nice day.

 

(CID:125212994)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2023-10-22 01:51 AM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2023-10-22 01:51 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore