Hi All,
We installed Netbotz 170 Rack access kit on Netbotz 570. We can take report form Handle(Up/down),Lock Status (Locked/Unlocked), Door(Open/Closed), Reader(Enabled/Disabled).
We also identified Card's to our employers. We can also open the rack with these cards. But we can't see the logs Who is accessed the doors and which time. Can we see this from DCE or Netbotz?
Best Regards,
Barlas.
(CID:150733160)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:06 PM . Last Modified: 2024-04-03 12:14 AM
Hi Barlas,
These logs are not available in DCE at this time. You must log in to the NetBotz appliance using Advanced View. Look under the "Tools" menu and "Appliance Event Log"
Thanks,
Steve
(CID:151060571)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:06 PM . Last Modified: 2024-04-03 12:14 AM
Hi Barlas,
These logs are not available in DCE at this time. You must log in to the NetBotz appliance using Advanced View. Look under the "Tools" menu and "Appliance Event Log"
Thanks,
Steve
(CID:151060571)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:06 PM . Last Modified: 2023-10-22 01:51 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.