I ran into an issue with DCE 7.4.1 backing up to windows 7. The share would mount successfully. Access from DCE is successful as the directory structure and files are created/transferred into the shared folder. DCE would mount the share and start the backup but intermittently fail, never completing. See below resolution.
The Console showed the below:
CIFS VFS:Unexpected lookup errror -12
CIFS VFS: cifs_mount failed w/return code = -12
The DCE server logs showed:
10/13/16 16:12:17.579 ERRR - Backup Log: rsync: mkstemp "/data/mount/backup/backup_DCEStokeCC_20161013151356_7.4.1/data/local/sensor2/B83972A/B83972A_nbAlinkEnc_0/2015/.sensor.194.rL5HFg" failed: Cannot allocate memory (12)(com.netbotz.server.services.backup.impl.BackupJob)
The issue is because Windows 7 is not initially optimized as a file server and requires manual registry changes.
Applicable Registry key description:
HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Services\lanmanserver\parameters\size
Your choices for this registry key are 1, 2 and 3.
1 = Minimize Memory Used
2 = Balance
3 = Maximize Throughput for File Sharing and Maximize
Throughput for Network Applications
HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Control\SessionManager\MemoryManagement\LargeSystemCache
Your choices for this registry key are 0 and 1.
1 = Maximize Throughput for File Sharing
0 = Maximize Throughput for Network Applications
To apply the changes follow the below process:
Press the CTRL + ESC – type “regedit.exe” – press enter
Navigate to:
HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Services\lanmanserver\parameters\size
Double click size and change hexadecimal value to 3
Navigate to:
HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Control\SessionManager\MemoryManagement\LargeSystemCache
Double click size and change hexadecimal value to 1
Reboot the Windows 7 system.
(CID:108828390)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:59 AM . Last Modified: 2023-10-22 01:50 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.