EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:38 PM . Last Modified: 2024-04-05 12:10 AM
Hello,
All my devices just went into failure mode. I have seen this before when the dhcp logs filled up and couldn't store more info so they all went into failure. I thought this issue was going to be fixed in 7.4.3 (which I am running). I just check the logs on the server and I am seeing this:
4/17/18 13:49:40.979 WARN - Unable to parse DHCP lease
java.lang.NullPointerException at com.netbotz.server.services.dhcp.impl.LeasesFileProcessor.parseLeasesFile(LeasesFileProcessor.java:216)
at com.netbotz.server.services.dhcp.impl.DhcpLeaseServiceImpl.parseLeasesFile(DhcpLeaseServiceImpl.java:77)
at com.netbotz.server.services.dhcp.impl.LeasesFileProcessJob.executeInternal(LeasesFileProcessJob.java:58)
at org.springframework.scheduling.quartz.QuartzJobBean.execute(QuartzJobBean.java:86)
at org.quartz.core.JobRunShell.run(
JobRunShell.java:202) at org.quartz.simpl.SimpleThreadPool$WorkerThread.run(SimpleThreadPool.java:534)
Any help would be great
Thanks inadvance
(CID:130096358)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:38 PM . Last Modified: 2024-04-05 12:10 AM
Hi Ryan, I am seeing that this was fixed in 7.5.0, not 7.4.3. We adjusted log rotation to prevent this scenario.
Tech support can help you obtain 7.5.0 and/or clean out the logs on v7.4.3 if need be.
(CID:130096365)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:38 PM . Last Modified: 2024-04-05 12:10 AM
Hi Ryan, I am seeing that this was fixed in 7.5.0, not 7.4.3. We adjusted log rotation to prevent this scenario.
Tech support can help you obtain 7.5.0 and/or clean out the logs on v7.4.3 if need be.
(CID:130096365)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:38 PM . Last Modified: 2023-10-22 01:49 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.