DCO access issues

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO access issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

0 Likes
7
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

DCO access issues

Earlier this morning we have had issues connecting to DCO.  The system was working today and failed about 10:07.  This is not a new install and there have been no access issues recently - before today.  We are running 8.2.2.

 

Firstly we contacted the AD support internally but this has not revealed any problems with the authentication server.

 

I have tried to access the desktop client without any success and get the reply "The credentials you have entered are invalid for this Struxureware Data Center Operation server".  I have not closed the web client that I had running and this still continues to function with multiple searches etc.

(CID:144868480)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

0 Likes
0
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Nigel,

Do I understand correctly you are unable to log in via desktop client? 

If yes, can you log in (or re-log in) via web client? 

Can you log in from another client/work station?

Since you mentioned contacting your AD support internally, then I guess the log in issue is with a remote user. Do you know if other remote/AD users having a similar login issue? 

Have you tried to log in by using a local user?

Have you verified if the server/application is running? (it can be verified via server webmin interface, StruxureWare DC Operation > Status).

Kind regards

(CID:144868562)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

0 Likes
0
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Jef,

Do I understand correctly you are unable to log in via desktop client? Correct - cannot log in to the desktop client.

If yes, can you log in (or re-log in) via web client? I do not want to log out - but no other users (including other admins) can log in to the web client so I presume I would be no different.

Can you log in from another client/work station?  This is not just me.  All my users are asking me if DCO is online.

Since you mentioned contacting your AD support internally, then I guess the log in issue is with a remote user. Do you know if other remote/AD users having a similar login issue? As said, this applies to all users.  DCO is offline.

Have you tried to log in by using a local user? No

Have you verified if the server/application is running? (it can be verified via server webmin interface, StruxureWare DC Operation > Status). Yes.  Status reports: 

Web Status Running
Application Status Running
Database Status Running alone

(CID:144868568)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

0 Likes
3
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Nigel,

According to your status page, DCO dose not seem to be offline.

Can you log in using a local user?

 

Since the log in issue is with remote users, then most likely there might have been some changes on the AD server. 

Assuming the AD server is accessible, then please try this:

Log in to web client by using a local admin user.

Go to Administration (top-right wheel icon) > Authentication Servers, 

edit the integrated AD server

check the settings, username/password, etc. and then click on the OK button. 

That should update the communication between the servers (AD and DCO).

 

Kind regards

(CID:144868640)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

In response to DCIM_Support
0 Likes
0
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

Thanks Jef.  This worked.  I luckily left the web client open and did not log out.  I entered "ok" and it forced the reset.  Now users are logging in again.  I will ensure a local user is effected for future use.

I would like to know how/what happened today, the AD people here say no changes were made (e.g. certificates) and I know we did not change DCO.  Would the log files reveal anything?

(CID:144868643)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

In response to DCIM_Support
0 Likes
0
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Nigel,

Sounds great that it helped. 

DCO log files may/can not tell what might have been changed on the AD side, however we can take a look at your logs (server logs + client application.log file) to see if they contain anything useful, thanks.

Kind regards

(CID:144868650)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

In response to DCIM_Support
0 Likes
0
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Nigel,

Many thanks for providing the log files. It seems issue was basically related to certificate change on AD server - more details provided by direct email, thanks. 

Kind regards

(CID:144869381)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2023-10-22 01:42 AM

0 Likes
0
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:55 PM . Last Modified: ‎2023-10-22 01:42 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore