DCO Upgrade 8.2.12 to 8.3.2 failed

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO Upgrade 8.2.12 to 8.3.2 failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:36 PM . Last Modified: ‎2024-04-03 12:04 AM

0 Likes
4
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:36 PM . Last Modified: ‎2024-04-03 12:04 AM

DCO Upgrade 8.2.12 to 8.3.2 failed

I have similar issue like described in this thread:

DCO Upgrade 8.2.7 to 8.3 failed

I have DCO 8.2.12 and would like to upgrade 8.3.2. In my case the following checkbox was active and checked like this:

Do not download packages from the Internet X

 

No thirdparty RPMs" stayed empty.

I read carefully the relevant documentation: Getting from previous versions to DCO 8.x and especially section of Upgrading using the latest 8.x iso file

Chapter 2.d. says:

"Selecting not to download from the Internet may be relevant if you know you don't have an Internet connection during the upgrade as it may be a bit quicker when the upgrade doesn't check for newer files online."

 

That is the reason why I checked. I know that snippet from the log is not always useful but let's make a try. I can see that some package updates was unsuccessful like:

Nov 20 10:58:36  operations-upgrade[15460]: Error: Package: 7:device-mapper-event-1.02.146-4.el7.x86_64 (@DCO-CentOS)
Nov 20 10:58:36 operations-upgrade[15461]: Requires: device-mapper = 7:1.02.146-4.el7
Nov 20 10:58:36 operations-upgrade[15462]: Removing: 7:device-mapper-1.02.146-4.el7.x86_64 (@DCO-CentOS)
Nov 20 10:58:36 operations-upgrade[15463]: device-mapper = 7:1.02.146-4.el7
Nov 20 10:58:36 operations-upgrade[15464]: Updated By: 7:device-mapper-1.02.149-10.el7_6.7.x86_64 (thirdparty-swdco-local-rpms)
Nov 20 10:58:36 operations-upgrade[15465]: device-mapper = 7:1.02.149-10.el7_6.7
Nov 20 10:58:36 operations-upgrade[15466]: Error: Package: dracut-config-rescue-033-535.el7_5.1.x86_64 (@DCO-CentOS)
Nov 20 10:58:36 operations-upgrade[15467]: Requires: dracut = 033-535.el7_5.1
Nov 20 10:58:36 operations-upgrade[15468]: Removing: dracut-033-535.el7_5.1.x86_64 (@DCO-CentOS)
Nov 20 10:58:36 operations-upgrade[15469]: dracut = 033-535.el7_5.1
Nov 20 10:58:36 operations-upgrade[15470]: Updated By: dracut-033-554.el7.x86_64 (thirdparty-swdco-local-rpms)
Nov 20 10:58:36 operations-upgrade[15471]: dracut = 033-554.el7
Nov 20 10:58:36 operations-upgrade[15472]: Error: Package: dracut-network-033-535.el7_5.1.x86_64 (@DCO-CentOS)
Nov 20 10:58:36 operations-upgrade[15473]: Requires: dracut = 033-535.el7_5.1
Nov 20 10:58:36 operations-upgrade[15474]: Removing: dracut-033-535.el7_5.1.x86_64 (@DCO-CentOS)
Nov 20 10:58:36 operations-upgrade[15475]: dracut = 033-535.el7_5.1
Nov 20 10:58:36 operations-upgrade[15476]: Updated By: dracut-033-554.el7.x86_64 (thirdparty-swdco-local-rpms)
Nov 20 10:58:36 operations-upgrade[15477]: dracut = 033-554.el7

 

and then which clearly says what is happened: (nothing)

 

Nov 20 10:58:38  operations-upgrade[14109]: Operations::UpgradeManager::runUpgradeLocal Upgrade process went from 8.2.12-80089 -> 8.2.12-80089
Nov 20 10:58:38  operations-upgrade[14109]: Operations::UpgradeManager::runUpgradeLocal The upgrade process did not result in a new version of dco.
Nov 20 10:58:38  operations-upgrade[14109]: Operations::UpgradeManager::runUpgradeLocal The upgrade process has completed

What am I doing wrong?

I already opened case with ID #65207401 and log/backup already uploaded to appbox of Schneider customer service rep.

(CID:152077451)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:36 PM . Last Modified: ‎2024-04-03 12:04 AM

0 Likes
2
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:36 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Mate,

It turns out that upgrading to 8.3.2 requires the DCO server having Internet access. Due to package dependencies an offline upgrade may fail, and unfortunately we have no work-around for this. In this case, eg. if the server dose not have Internet access, go for: a) clean installation of 8.3.2 b) and then restoring the latest backup file.

Kind regards

(CID:152077465)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:36 PM . Last Modified: ‎2024-04-03 12:04 AM

0 Likes
2
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:36 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Mate,

It turns out that upgrading to 8.3.2 requires the DCO server having Internet access. Due to package dependencies an offline upgrade may fail, and unfortunately we have no work-around for this. In this case, eg. if the server dose not have Internet access, go for: a) clean installation of 8.3.2 b) and then restoring the latest backup file.

Kind regards

(CID:152077465)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

In response to DCIM_Support
0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

Thanks Jef, upgrade was successful with enabling (and setting up) internet access. I don't know why it is not possible to compile iso with all the necessary files to in-place upgrade but in this case maybe it would worth to post it for the future releases: internet access is necessary.

(CID:152077910)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

In response to DCIM_Support
0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Mate,

Glad to hear that you've successfully upgraded, many thanks for the update and suggestion (it will be added to the upgrade page soon), thanks.

Kind regards

(CID:152078330)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2023-10-22 01:41 AM

0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2023-10-22 01:41 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore