DCO Server issue

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO Server issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

0 Likes
7
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

DCO Server issue

 


Dear Support team ,

Greetings! We have issue here on one of the site where the sales team has shared the solution with the below DCO server to customer & now we cannot configure our DCO on this server. It is not supporting our Operating system.

Pls advise?
Meanwhile, we have requested the customer to replace the server with RED hatt. server with the config matching our DCO, but he needs an confirmation email on the subject.

Server details.
CPU: 8 cores
Memory: 16 GB RAM
100 GB storage, speed minimum 170 MB/s

Provide any machine which complies with these specs. If your presales team confirms that the below SKUs comply with the aforementioned requirements, please to provide the same to IBM asap and lets close the subject matter;
SKU Description Q-ty
SR730-E5-2630V3
Rail & cable PowerEdge R730 :Intel Xeon E5-2630v3 2.4GHz,20MCache,8.00GT/s QPI,Turbo,HT,8C/16T(85W) Max Mem 1866MHz,2X 8 GBRDIMM, 2133 MT/s, Dual Rank, x4 Data Width,VFlash, 8 GB SD Card for iDRAC Enterprise,PERC H730Integrated RAID Controller, 1GBCache, No Hard Drive, Dual, Hot-plug, Redundant Power,3Yr -NBD. 1
370-ABUN 8GB RDIMM,2133MT/s, DualRank. 1
400-AEEK 300GB 15KRPM SAS 6Gbps 2.5in Hot-plug Hard Drive,3.5in HYB CARR,13G,CusKit 1



 

(CID:105465964)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

0 Likes
5
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

The system requirements depend on the size of the solution, see System Requirements for details.

The Debian version of DCO 7.5 is a .iso file, complete with operating system and all, that you will install on the system.

The Red Hat version is an application package (.rpm file) for Red Hat Enterprise Linux 6.

(CID:105465973)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

In response to DCIM_Support
0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

Thanks for the email. The issue here is when our FSR try to install the DCO with the server supplied, it doesn't detect the hardware. All the methadology is applied but its No success.  It doesnot supportin linux 6. Pls advise solution or do we have to recommend them to order new server Red hat which supports linux 6.

Thanks to respond

Yasser

Schneider Electric

(CID:105465999)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

In response to DCIM_Support
0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

I'm not sure I understand if you are trying to install the ISO (with Debian)? If that's the case, then you may try installing using alternative drivers which support newer hardware. See http://dcimsupport.apc.com/display/UAOp74/Installing+StruxureWare+Data+Center+Operation#InstallingSt...

(CID:105466000)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

In response to DCIM_Support
0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

After many attempts to install DCO system using USB bootable image and DVD, with no luck because of system miss compatibility with the server hardware. So after our discussions as per your request to move to installing DCO system on ESXi hypervisor and install DCO system on Virtual Machine to avoid the hardware miss compatibility in order to complete the DCO installation. The installation has been successful with the following below: - ESXi 6 u1 installed as a hypervisor on the server with IP address x.x.x.201 o Esxi username: root o Esxi password: xxxx - DCO has been installed on ESXi with IP address x.x.x.205 o DCO username: apc o DCO password: xxx The user will connect to DCO system from web interface with IP address x.x.x.205 as per attached file. Note: ESXi 6 is on trial version which is valid only for 60 days. Prior to this period ends you need get the required license. .

(CID:105466003)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

In response to DCIM_Support
0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:57 PM . Last Modified: ‎2024-04-09 01:03 AM

The license has expired and now the server supplier s charging usfor the license. Pls advise?

(CID:105466004)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:58 PM . Last Modified: ‎2024-04-09 01:03 AM

In response to DCIM_Support
0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:58 PM . Last Modified: ‎2024-04-09 01:03 AM

Hi Mohammad, You can follow this guide on how to get and install a free license for ESXi 6. http://www.vmwarearena.com/vsphere-6-0-download-free-esxi-6-0-license-keys/

(CID:105466005)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:58 PM . Last Modified: ‎2023-10-31 10:52 PM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:58 PM . Last Modified: ‎2023-10-31 10:52 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore