DCO LAB Room Copy Function Not Working For All Rooms

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO LAB Room Copy Function Not Working For All Rooms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:14 AM

0 Likes
4
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:14 AM

DCO LAB Room Copy Function Not Working For All Rooms

Currently using Version 7.4.5

Found that not all rooms are able to be copied and pasted into another location.

The copy function is visible on the menu and you can click the copy item, but the room does not show up in the clipboard section.

Some rooms work in this way and some do not. A new room that was created in Lab since upgrading to 7.4.5 and does not copy. Frustrating thing is that there is no error indicating why it wont copy.

Below is the client application log entry created when copy is clicked for the room.

2015-03-18 07:53:04,934 ERROR [com.apc.sma.client.Application$EclipseToLog4jLogListener] (main) Unhandled event loop exception [org.eclipse.core.runtime]

com.apc.config.utils.hibernate.HibernateMappingLookupException: No Hibernate mapping for class com.apc.config.isxdesignermodel.impl.serverroom.TileGridImpl_$$_javassist_6
at com.apc.config.utils.hibernate.HibernateMappingLookup.getPersistentClassOrFail(HibernateMappingLookup.java:95)
at com.apc.itil.smacore.internal.copy.CopyServiceImpl.copyValues(CopyServiceImpl.java:305)
at com.apc.itil.smacore.internal.copy.CopyServiceImpl.getCopiedValue(CopyServiceImpl.java:383)
at com.apc.itil.smacore.internal.copy.CopyServiceImpl.copyValues(CopyServiceImpl.java:316)
at com.apc.itil.smacore.internal.copy.CopyServiceImpl.populateAll(CopyServiceImpl.java:417)
at com.apc.itil.smacore.internal.copy.CopyServiceImpl.deepCopy(CopyServiceImpl.java:578)
at com.apc.itil.smacore.internal.copy.CopyServiceImpl.copy(CopyServiceImpl.java:618)
at com.apc.itil.smacore.internal.copy.CopyServiceImpl.copy(CopyServiceImpl.java:628)
at com.apc.itil.smacore.internal.copy.CopyBoardImpl.copy(CopyBoardImpl.java:173)
at com.apc.dcoverview.internal.handlers.CopyHandler.execute(CopyHandler.java:10)
at com.apc.dcoverview.internal.handlers.AbstractCutCopyHandler.execute(AbstractCutCopyHandler.java:39)
at org.eclipse.ui.internal.handlers.HandlerProxy.execute(HandlerProxy.java:293)
at org.eclipse.core.commands.Command.executeWithChecks(Command.java:476)
at org.eclipse.core.commands.ParameterizedCommand.executeWithChecks(ParameterizedCommand.java:508)
at org.eclipse.ui.internal.handlers.HandlerService.executeCommand(HandlerService.java:169)
at org.eclipse.ui.internal.handlers.SlaveHandlerService.executeCommand(SlaveHandlerService.java:241)
at org.eclipse.ui.internal.handlers.SlaveHandlerService.executeCommand(SlaveHandlerService.java:241)
at org.eclipse.ui.menus.CommandContributionItem.handleWidgetSelection(CommandContributionItem.java:829)
at org.eclipse.ui.menus.CommandContributionItem.access$19(CommandContributionItem.java:815)
at org.eclipse.ui.menus.CommandContributionItem$5.handleEvent(CommandContributionItem.java:805)
at org.eclipse.swt.widgets.EventTable.sendEvent(EventTable.java:84)
at org.eclipse.swt.widgets.Widget.sendEvent(Widget.java:1053)
at org.eclipse.swt.widgets.Display.runDeferredEvents(Display.java:4165)
at org.eclipse.swt.widgets.Display.readAndDispatch(Display.java:3754)
at org.eclipse.ui.internal.Workbench.runEventLoop(Workbench.java:2701)
at org.eclipse.ui.internal.Workbench.runUI(Workbench.java:2665)
at org.eclipse.ui.internal.Workbench.access$4(Workbench.java:2499)
at org.eclipse.ui.internal.Workbench$7.run(Workbench.java:679)
at org.eclipse.core.databinding.observable.Realm.runWithDefault(Realm.java:332)
at org.eclipse.ui.internal.Workbench.createAndRunWorkbench(Workbench.java:668)
at org.eclipse.ui.PlatformUI.createAndRunWorkbench(PlatformUI.java:149)
at com.apc.sma.client.Application$2.run(Application.java:276)
at com.apc.sma.client.Application$2.run(Application.java:1)
at java.security.AccessController.doPrivileged(Native Method)
at javax.security.auth.Subject.doAs(Unknown Source)
at com.apc.sma.client.Application.start(Application.java:279)
at com.apc.isxo.client.bootstrap.BootstrapApplication.start(BootstrapApplication.java:119)
at org.eclipse.equinox.internal.app.EclipseAppHandle.run(EclipseAppHandle.java:196)
at org.eclipse.core.runtime.internal.adaptor.EclipseAppLauncher.runApplication(EclipseAppLauncher.java:110)
at org.eclipse.core.runtime.internal.adaptor.EclipseAppLauncher.start(EclipseAppLauncher.java:79)
at org.eclipse.core.runtime.adaptor.EclipseStarter.run(EclipseStarter.java:344)
at org.eclipse.core.runtime.adaptor.EclipseStarter.run(EclipseStarter.java:179)
at sun.reflect.NativeMethodAccessorImpl.invoke0(Native Method)
at sun.reflect.NativeMethodAccessorImpl.invoke(Unknown Source)
at sun.reflect.DelegatingMethodAccessorImpl.invoke(Unknown Source)
at java.lang.reflect.Method.invoke(Unknown Source)
at org.eclipse.equinox.launcher.Main.invokeFramework(Main.java:622)
at org.eclipse.equinox.launcher.Main.basicRun(Main.java:577)
at org.eclipse.equinox.launcher.Main.run(Main.java:1410)

(CID:95355326)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:13 AM

0 Likes
1
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:13 AM

Hi Richard,

The problem seen here was in regards to the copy functionality not handling some elements of an upgraded room in DCO Lab correctly. 

Since the issue only occur in DCO Lab we have created a patch for this that can be applied to the client PC(s) running DCO Lab. The patch need to be applied to all client PCs running DCO Lab.

The patch must replace the existing files of the same name in the dropins folder after the DCO Lab client has been opened once. The dropins folder is located in the installation folder of the DCO Lab client (using windows: C:\Program Files\StruxureWare Data Center Operation Lab 7.4.5\application\dropins)

The patch will also be included in the next release of DCO.

I will provide the patch file to you offline.

 

Should this be experienced by others feel free to contact us in order to get it resolved as well.

(CID:95355422)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:14 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:14 AM

Hi Richard, We are investigating the issue and is currently able to reproduce your scenario. We will get back to you once we have more information on how this is solved.

(CID:95355375)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:13 AM

0 Likes
1
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:13 AM

Hi Richard,

The problem seen here was in regards to the copy functionality not handling some elements of an upgraded room in DCO Lab correctly. 

Since the issue only occur in DCO Lab we have created a patch for this that can be applied to the client PC(s) running DCO Lab. The patch need to be applied to all client PCs running DCO Lab.

The patch must replace the existing files of the same name in the dropins folder after the DCO Lab client has been opened once. The dropins folder is located in the installation folder of the DCO Lab client (using windows: C:\Program Files\StruxureWare Data Center Operation Lab 7.4.5\application\dropins)

The patch will also be included in the next release of DCO.

I will provide the patch file to you offline.

 

Should this be experienced by others feel free to contact us in order to get it resolved as well.

(CID:95355422)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:13 AM

In response to DCIM_Support
0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:32 AM . Last Modified: ‎2024-04-10 12:13 AM

Hi Soren, thank you once again for your follow-up and patch to resolve this issue. I have installed the patch and can confirm that the LAB room copy issue has now been resolved.

(CID:95355489)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:33 AM . Last Modified: ‎2023-10-31 10:50 PM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:33 AM . Last Modified: ‎2023-10-31 10:50 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of