DCO 8.3.2 support on Portal 1.3.7

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO 8.3.2 support on Portal 1.3.7
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:12 PM . Last Modified: ‎2024-04-03 12:33 AM

0 Likes
8
2556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:12 PM . Last Modified: ‎2024-04-03 12:33 AM

DCO 8.3.2 support on Portal 1.3.7

Dear Community, 

 

We have recently upgraded to DCO 8.3.2 from DCO 8.2.12. We found that values from DCO was not able to display properly and it runs until "timeout". However, values from DCE has no issue. 

 

Does anyone have any idea on this? 

Best Regards, 

 

TJ

(CID:148770719)

Labels
  • Labels:
  • Data Center Operation
  • Portal
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

0 Likes
6
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

Hi TJ,

Your portlets are getting timeout - it seems your Portal is not able to communicate with its integrated DCO. That might be network related or possibly configuration issue. Check the settings/configuration in Portal: "Go to" > Control Panel > Connect to StruxureWare system. I would either edit the current integrated server and/or re-add and reconfigure the portlets. Make sure the "Endpoint URL" correctly defined and credentials (User Name/Password) are correct:

 

Kind regards

(CID:148770846)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

0 Likes
6
2555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

Hi TJ,

Your portlets are getting timeout - it seems your Portal is not able to communicate with its integrated DCO. That might be network related or possibly configuration issue. Check the settings/configuration in Portal: "Go to" > Control Panel > Connect to StruxureWare system. I would either edit the current integrated server and/or re-add and reconfigure the portlets. Make sure the "Endpoint URL" correctly defined and credentials (User Name/Password) are correct:

 

Kind regards

(CID:148770846)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

In response to DCIM_Support
0 Likes
0
2556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

Hi Jef, 

What is the port used between DCO and Portal connection? Just want to make sure Portal server allows the port traffic

 

BR, 

 

TJ.

(CID:148770928)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

In response to DCIM_Support
0 Likes
0
2556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

Hi TJ,

My above illustration is showing that as well 😀 , Communication between Portal and DCO can be via port 8080 (http) and/or 443 (https).

So when defining the Endpoint URL, you would need to enter:

http://:8080

or

https://:443

 

You might also want to check if your DCO accepts http and/or https connections. To verify this, go to DCO Webmin interface, StruxureWare DC Operation > Setup.

Kind regards

(CID:148771201)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

In response to DCIM_Support
0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

Hi Jef, 

Those site are connected before and running well.  Below are the things I checked:

  1. DCO setup page - http and https accepted. 
  2. Disabled firewall in Portal server - same result. 
  3. One of the DCO sites was connected via APC LAN (192.168.x.x), but it also shows the same issue. 
  4. Checked java version - Ver7 update 79, not sure if this causes the issue? 
  5. Tried the endpoint to format https://:443 for all DCO sites but not working. 

So I am still wondering which part might be gone wrong...

 

BR

TJ

 

(CID:148771589)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

In response to DCIM_Support
0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

Hi TJ,

It seems the Java version is okay (it is similar to my test setup).

Verify if the servers (DCO and Portal) are reachable (ex: ssh log in DCO and ping to Portal server or vice versa), eg. if they can communicate.

Try adding/configuring a new DCO connection in Portal (instead of modifying the existing one) and see if that works - and make sure the endpoint url is properly set and also verify the credentials are correct.

Kind regards

(CID:148771595)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

In response to DCIM_Support
0 Likes
0
2556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:33 AM

 

Hi Jef,

 

Update from my attempt:

  1. Actually there are 3 DCO sites connected to the Portal. One of the sites is running quite slow when we open the DCO webpage of it. 
  2. After I remove this site from the list, it seems that the other 2 sites' data are able to load very fast. 

I am guessing the slow loading DCO have caused this issue. 

Since this one issue is identified, I may need to check why is the other DCO is running very slow...

BR, 

 

TJ 

(CID:148771662)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:32 AM

In response to DCIM_Support
0 Likes
0
2556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2024-04-03 12:32 AM

Hi TJ,

Great, many thanks for the update.

Kind regards

(CID:148771667)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2023-10-22 01:34 AM

0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:13 PM . Last Modified: ‎2023-10-22 01:34 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore