Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

DCO 8.0 Single phase modelling

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO 8.0 Single phase modelling
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

0 Likes
6
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

DCO 8.0 Single phase modelling

The release notes say that 2 new features I have always been interested in are now available.

  • Modelling of single phase UPS.
  • Starting a power path from a PDU instead of a UPS.

Single phase UPS modelling

What I cannot figure out how to do is model a single phase rack mounted UPS - the power option is absent from any I have chosen in the genome of 8.0.  I specifically wanted to model a Symmetra LX 16000 but have been unable to figure out how.

Starting a power path from a PDU instead of a UPS.

I cannot figure out how to do this full stop.  I can create power paths below the PDU but on the PDU I cannot define them as A and B supplies.


I could not find anything in the DCO documentation or tutorials that explaining either of these.

Any pointers on either of these please?

(CID:106209335)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2024-04-08 11:44 PM

0 Likes
1
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2024-04-08 11:44 PM

You cannot define the PDU as either A-feed or B-feed. That options is available only for UPSs and Recitifiers (for DC).

It is however no longer necessary to mark the feeds as A or B for the capacity calculations to run. To make sure the PDU defines a capacity for the calculations remember to set an input breaker for the PDU.

(CID:106209382)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

0 Likes
2
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

Hi Garry!

Unfortunately rack-mounted  UPS are still unsupported. New version supports single phase floor-mounted UPS.

I'm not sure about second question - have not touch new version myself.

(CID:106209343)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

In response to DCIM_Support
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

Thanks Valentin. I don't suppose you know if there will be support for single phase rack mount UPS soon do you?

(CID:106209397)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

In response to DCIM_Support
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:10 AM . Last Modified: ‎2024-04-08 11:44 PM

No, I don't know.

(CID:106209512)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2024-04-08 11:44 PM

0 Likes
1
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2024-04-08 11:44 PM

You cannot define the PDU as either A-feed or B-feed. That options is available only for UPSs and Recitifiers (for DC).

It is however no longer necessary to mark the feeds as A or B for the capacity calculations to run. To make sure the PDU defines a capacity for the calculations remember to set an input breaker for the PDU.

(CID:106209382)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2024-04-08 11:44 PM

In response to DCIM_Support
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2024-04-08 11:44 PM

Thanks for the answer. I just expected that you would be able to define A and B supplies but could not figure out how to do it. At least I know the reason why now..

(CID:106209396)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2023-10-31 10:47 PM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:11 AM . Last Modified: ‎2023-10-31 10:47 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of