DCO 7.3.6 client giving error in Win7 64 bit

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO 7.3.6 client giving error in Win7 64 bit
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:06 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
12
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:06 AM . Last Modified: ‎2024-04-10 01:00 AM

DCO 7.3.6 client giving error in Win7 64 bit

DCO 7.3.6 when installing on Windows 7 64 bit giving error. please advise?

32 bit installation is working fine.

DCO 7.3.6 Client Error.jpg

(CID:93913977)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:06 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:06 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Shemil, I guess you are installing as administrator? I'm a bit worried about the folder called homes$. I'm not sure if that might cause trouble for our installation? When are you seeing the error message, while installing, logging in or starting the client? Please attach the mentioned log file to the question above. That will help investigation further. Also if the error occurs while logging in to the system please attache the server log files that can be gathered using the server configuration interface https://:10000 StruxureWare Data Center Operation>Download server log files

(CID:93913992)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:06 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:06 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Soren, Yes the DCO client is installed as administator.The error comes when logging in after entering the IP, username and password. The system gets stuck in "Initializing Application" and afterwards the error pops up. The server log file is around 30mb and in the site for security reasons they can't share any file with us in USB or in dropbox. Thanks & Regards Shemil

(CID:93914064)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

The path in the screenshot tells us that the user folder is located on a network share. That may work fine but unless we get the client log file, it is very hard to come up with an explanation (and a solution).

(CID:93914144)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Shemil, It is fine to start with the client log that is mentioned in the screenshot you posted in the initial question. The log file should in your case be located in \\users\homes$\7701590\.isxo\7.3.6-86630\Operations\.metadata\.log When you state it is working on 32-bit is the client installed in the same folder?

(CID:93914328)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

For the 32 bit client it is in different folder C:\Users\6962\.isxo\7.3.6-86630\Operations\.metadata\.log is this because of JMS binding and JMS control ports 4457 & 4460 being blocked from Firewall. I thought of this but they tested Telnet from the 64 bit PC to these ports and its working. Also the 32 bit client is also on the same vlan.

(CID:93914597)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Shemil, it seems like the 64bit version for some reason is installed on a network shared folder and that is causing problems? If possible try to install the 64 bit locally on the client machine. Since the 32 bit version is working and based on your comment seems to be installed in a local folder trying to install the 64bit locally would be the next step as I see it. Also make sure the network settings are the same for the 2 client machines. Fianally please share the mentioned log file from the 64bit machine that is failing if that is still the case when installed locally.

(CID:93914625)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Soren, We created a new VM for Win7 64 bit and also added a user local to the machine and it is working fine. Now what we noticed is that there are users who are using VDI (Virtual desktops) using Cirtix and as per group policy a Universal profile manager manages all their profiles in users\homes$ shared folder. We checked the installation and it is happening locally in C:\ program files folder for all users. But if a user has profile in the shared folder users\homes$\ folder then it is not working even if the software is installed in local folder.

(CID:93914794)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

0 Likes
3
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Soren,

We created a new VM for Win7 64 bit and also added a user local to the machine and it is working fine. Now what we noticed is that there are users who are using VDI (Virtual desktops) using Cirtix and as per group policy a Universal profile manager manages all their profiles in users\homes$ shared folder. We checked the installation and it is happening locally in C:\ program files folder for all users. But if a user has profile in the shared folder users\homes$\ folder then it is not working even if the software is installed in local folder.

I am attaching the log from client found in users\homes$ shared folder.

(CID:93914796)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

In response to DCIM_Support
0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Shemil, From the log file it seems like the user do not have full write access to the network folder. This will give all sorts of errors when launching the client. It might be worth trying if possible to rename the folder to not including $ or if possible map the network drive to a local drive.

(CID:93914852)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

In response to DCIM_Support
0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Soren, We tested with a user having write access to the shared folder and for him also it did not work. Also please clarify how the log file is written in "users\homes$\7638\.isxo\7.3.6-86630\Operations\.metadata\.log" if the user (7638) does not have write permission? I checked with the client to change folder name to remove $ sign and it is not possible from their side since they have around 200 live users accessing VDI. We also tried mapping the network drive to a local drive and it also did not give any result. Does Operations client have any condition or scripting written in Java that the user have to be local admin with his profile stored in C:\users directory? Does Operations client support Virtual PC with Microsoft Roaming profile environment where VDI (Citrix) manages user profiles and it will be in a shared folder? Thanks & Regards Shemil

(CID:93915190)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

In response to DCIM_Support
0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:07 AM . Last Modified: ‎2024-04-10 01:00 AM

Hi Shemil, I'm not an expert in these virtual desktop environments and to my understanding they are fairly complex to manage. I would imagine that the user rights can be administered at different levels giving access to some operations of various files and others not. The only requirement for administrative rights are during installation. In regards to Microsoft Roaming profile environment where VDI (Citrix) manages user profiles this has not been tested in our test environment and therefore we can say this is supported. However I am aware a virtual desktop environment has been made running, I do not know of the details though.

(CID:93915191)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:08 AM . Last Modified: ‎2023-10-31 10:46 PM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:08 AM . Last Modified: ‎2023-10-31 10:46 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of