DCE unresponsive

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE unresponsive
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

0 Likes
5
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

DCE unresponsive

Hello.

I am trying to access to DCE though the client but after a long period of time the client closes without prompting any output. I have also tried to connect to DCE through the web interface but after period of time, it shows the following message...

I have checked the virtual appliance and its running OK, I can also log through the console:

Is there any way to troubleshoot this (log files, diagnostic tools,...) or any workaround available? It's safe to reboot the virtual appliance from vCenter in this state?

 

Thanks.

(CID:93193374)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

0 Likes
1
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

Hi Manuel,

 

You are unable to download the log files by typing in the IP address of the DCE server followed by /capture logs. (for instance /capturelogs). You might not be able to get the logs when the server is in this state. I would try to obtain the logs if possible before attempting to reboot the server (after a reboot we may not be able to see from the logs after the reboot what has caused the issue in the first place). 

Did the DCE VM suddenly just go into this state? Did you do an upgrade recently?

Yes, it is safe to reboot the DCE server VM through vCenter. 

Do you have a recently successful backup done on the DCE server? Hopefully this is stored on a remote storage system rather than locally. 

Do you have snapshots created? 

What are your VM specs for the DCE VM? Do you have enough HDD space for the DB to run correctly? Did you add additional HDD to the DCE VM setup? 

Are you aware of any changes made to the DCE server?

When you reboot the DCE VM, please watch the boot up sequence for any failed errors. 

 

Regards,

Breda

 

(CID:93193379)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

0 Likes
1
1325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

Hi Manuel,

 

You are unable to download the log files by typing in the IP address of the DCE server followed by /capture logs. (for instance /capturelogs). You might not be able to get the logs when the server is in this state. I would try to obtain the logs if possible before attempting to reboot the server (after a reboot we may not be able to see from the logs after the reboot what has caused the issue in the first place). 

Did the DCE VM suddenly just go into this state? Did you do an upgrade recently?

Yes, it is safe to reboot the DCE server VM through vCenter. 

Do you have a recently successful backup done on the DCE server? Hopefully this is stored on a remote storage system rather than locally. 

Do you have snapshots created? 

What are your VM specs for the DCE VM? Do you have enough HDD space for the DB to run correctly? Did you add additional HDD to the DCE VM setup? 

Are you aware of any changes made to the DCE server?

When you reboot the DCE VM, please watch the boot up sequence for any failed errors. 

 

Regards,

Breda

 

(CID:93193379)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

In response to DCIM_Support
0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

Thanks Breda, I rebooted the virtual appliance through vCenter and works fine. I have updated it a couple of days before the issue came up.

(CID:93193441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

Hi,

 

My problem Is same. My DCE was upgraded to ver. 7.2.4 before 1 month.

 I cant start my client and my web client. :

Data Center Expert is starting up. Please wait. This page will refresh every 10 seconds

 

The problem persist after rebooting of VM.

When VM is starting , I see some message about failed  sql database. 

 

(CID:93193387)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:31 AM . Last Modified: ‎2024-04-10 01:11 AM

Hi Ivaylo,

 

If you have a software support contract, you should be able to call tech support in your local region. They should be manually able to remote into your DCE server and restart the DB for you. Usually the reasons for the DB not being able to start is that there is not enough HDD allocated to the VM and it is full and cannot run the DB. What are the specs of your VM? How much RAM, HDD is allocated? Have you added any additional HDD to the DCE VM? Are you using remote or local storage? Have you any successful full backups created or snapshots that you can revert to? The other reason maybe that the DB is corrupt.

The first step is to contact local support to try and manually restart the DB for you. If that doesn't work, the best option is to revert back to an older backup or snapshot. Add some HDD (if there is not enough allocated), and see if the DCE server starts. 


Regards,

Breda

 

 

(CID:93193389)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:32 AM . Last Modified: ‎2023-10-31 10:44 PM

0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:32 AM . Last Modified: ‎2023-10-31 10:44 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore