Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

DCE sensor disappear after interval of time

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE sensor disappear after interval of time
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
79
APC_Steve
Commander APC_Steve Commander
55
gsterling
Commander gsterling Commander
50
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:24 PM

0 Likes
4
323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:24 PM

DCE sensor disappear after interval of time

This question was originally posted on DCIM Support by Gleb Tyunikov on 2019-09-25


Hello team,

Another question about a situation i am facing in DCE.

I discovered a PDU with a sensor chain of 3 sensors using my DCE server and for the first couple of minutes all seems to work fine, i did a few testing on the temperature and noticed that one of my temperature sensors is missing.

I check my other connected device and the same thing was happening over there with the same sensor.

I logged in to the PDU device to see if the problem was with the device but the data was there and it was live.

I tried to see maybe there some kind of issue with the sensor but after rediscovering it with DCE I can see for another few minutes and then it is disappearing again. 

 

Did anyone encounter something like this before?

 

Best regards and thanks

(CID:149291920)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:24 PM

0 Likes
0
323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:24 PM

This comment was originally posted on DCIM Support by spezialist on 2019-09-25


Dear Gleb Tyunikov,

What PDU model/type and which sensors? What does “disappear” mean - have they switched to Unplugged state? Can you attach a couple of screenshots from DCE and from PDU GUI?

With respect.

(CID:149291928)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:24 PM

0 Likes
0
323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:24 PM

This comment was originally posted on DCIM Support by Gleb Tyunikov on 2019-09-25


Thank you for the answer,

Unfortunately i cannot provide any screenshots but i will try and explain the issue.

Im using Raritan PX3 PDU with DPX-T3H1 sensors.

After discovery i can see 7 temperature lines


1 - Temperature 1 status = normal

2 - Temperature 1  degrees = 24 c

3 - Temperature 2 status = normal

4 - Temperature 2  degrees = 25 c

5 - Temperature 3 status = normal

6 - Temperature 3  degrees = 26 c

7 - External Temperature sensor = (value of sensor X for example-sensor 1)

 

after a few minutes it changes to this (as you can see now line 4 is not present) : 

1 - Temperature 1 status = normal

2 - Temperature 1  degrees = 24 c

3 - Temperature 2 status = normal

5 - Temperature 3 status = normal

6 - Temperature 3  degrees = 26 c

7 - External Temperature sensor = (value of sensor X for example sensor 1)

 

and the DCO sees the Temperature sensor 2 as the External sensor but it holds the degrees of sensor X (that is for example-sensor 1)

 

I hope this was helpfull

 

(CID:149291987)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:24 PM

0 Likes
0
323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:24 PM

This comment was originally posted on DCIM Support by spezialist on 2019-09-25


Dear Gleb Tyunikov,

Unfortunately i cannot provide any screenshots but i will try and explain the issue.

This is bad, since it is often better to see once than to hear many times. I hope you have full access to the DCE-server and PDU?

Can you say which DDF-files and which versions you use to discover the specified PDUs with sensors?

If you have installed DCE-7.6.0 and higher, then you can do snmpwalk on your problematic PDU twice with an interval of several minutes (see for example How to create an SNMP walk file in the Data Center Expert 7.6.x web client). Having received two snmpwalk files, you can compare them. This procedure must be done.

Please do this and report the result.

and the DCO sees the Temperature sensor 2 as the External sensor but it holds the degrees of sensor X (that is for example-sensor 1)

Perhaps this is a mistake and did you mean DCE?

With respect.

(CID:149292155)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:24 PM

0 Likes
0
323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:24 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc