DCE sends a Netbotz devices critical comunication error message

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE sends a Netbotz devices critical comunication error message
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

0 Likes
8
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

DCE sends a Netbotz devices critical comunication error message

Dear guys,

Our customer is worry because DCE is often sending a Netbotz devices critical comunication error message. The message in sent by email to the StruxureWare Data Center Expert administrators only.

The comunication error is auto solved after two or three seconds and the customer switch log is also reporting his problem. Actually it is happening with three devices, one 570, one 500 and one 355 devices. Also Netbotz devices hasn't any problem.

How can I know the cause of this problem and how and I solve it?

Best regards,

 

Enric

 

(CID:105466226)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

0 Likes
5
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

Dear Enric,

Here are my suggestions:

  • Please make sure that firewall settings or network issues do not block communication over port # 80 & Port # 443 between Struxureware DCE and Netbotz appliance
  • Please check the Netbotz appliance polling settings in DCE, and see if the same behavior with increased Poll rate  

  • I also would like to make sure that Netbotz appliance firmware and DCE version is the latest version
  • Make sure that the network settings such as DNS IP addresses are correct

Were the netbotz appliances detected via Port # 80? 

Are the netbotz appliances on the same network? 

Do you have any Netbotz which is communicating with DCE without loss of communication on the same network or different network? This can help you to figure if its related to network issue. 

It is also a good idea to see from when these loss of communication alerts started for netbotz appliance from DCE. Do you have any sensors not communicating with the netbotz appliance? Was there any changes made to the netbotz appliance? 

regards,

Bala

(CID:105466243)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

In response to DCIM_Support
0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

Dear Bala,

There are no issues with firewall and network with ports 80and 443.

The Netbotz Appliance Polling is set to 1 minute for data collection and 1 minute for monitoring. The customer wants this configuration and we cannot increase these values.

We have the latest version of Netbotz firmware and DCE.

All Netbotz appliance and DCE are in the same network and the customer has other Netbotz appliance in the same network wich doesn't loss communication.

When a communication is lost with a Netbotz, all sensors connected to this Netbotz also loss communication.

Maybe can help you an information. This morning I don a ping -t to some Netbotz and I've could see sometimes the response time was higher than 2500 ms. If you want I have the ping output in a text file.

Best regards,

 

Enric

 

(CID:105466981)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

In response to DCIM_Support
0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:04 AM . Last Modified: ‎2024-04-09 01:01 AM

As far as I know, Network latency which you mentioned is very high. Since Polling is set to 1 minute and if the Netbotz appliance is not able to respond to DCE polling, then DCE will respond with loss of communication or timed out errors. I think one of the reasons could be the Network or network traffic related.

(CID:105466982)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

In response to DCIM_Support
0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

Hi Bala, I understand your suggestions but this system has been running without any error for some months with the same transactions and now is getting these errors. The DCE version is 7.2.6, will be better to upgrade to 7.3.1?

(CID:105467380)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

In response to DCIM_Support
0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

Dear Bala, I've increased the polling time and also upgraded the DCE version to the last version (7.3.1) The Netbotz is already with the latest version (4.5.1) and the problem hasn't solved. The customer network team has checked the network and all it's right but the problem is still happening. How can we avoid this problem? Best regards, Enric

(CID:105468843)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

In response to DCIM_Support
0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

Hi guys!

I am having the some trouble with one of my costumers and I would like to know how Enric  solved is trouble, If its done could you help me solving the same trouble????

(CID:126182243)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2024-04-09 01:01 AM

Good Morning

some time ago I had the same problem and I was able to solve it by changing the MTU parameter in network settings, this parameter resizes the packages sent by netbotz.




 


 

 

 

(CID:129411361)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2023-10-31 10:44 PM

0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:05 AM . Last Modified: ‎2023-10-31 10:44 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.