Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

DCE periodically lost communication with SymmetraPX500 Virtual Display

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE periodically lost communication with SymmetraPX500 Virtual Display
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
76
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:22 PM

0 Likes
3
435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-03 06:22 PM

DCE periodically lost communication with SymmetraPX500 Virtual Display

This question was originally posted on DCIM Support by spezialist on 2017-07-25


Hi all!

Maybe not quite on the topic, but I found this bug with a DCE-server that not only monitors the NMC2 board of the Symmetra PX500 UPS, but also its Display (Virtual Display).

The bug periodically (almost every second month) occurs in this Symmetra PX500 UPS:

UPS firmware: 4.36.12
Display firmware: 2.5.2.116
Display hardware: 640-4729A
NMC2 firmware: 6.4.6
NMC2 hardware: 05

The essence of the bug #1: the Display and NMC2 board are periodically lost communication with the MIM and RIM of this UPS. For example, here is a part of the log from the Virtual Display with a mass of similar messages about Display communication:

And here example a part of the log from the same Virtual Display with a messages about NMC2 board communication:

And similar logs, but already from the NMC2 board with a mass of similar messages about Display communication:

And here example a part of the log from the same NMC2 board with a messages about NMC2 board communication and self reboot:

The NMC2 board is configured in 'rw' mode in this Symmetra PX500 UPS. This is done in order to perform periodic synchronization of Display RTC and correct switch to/from DST.

In addition, in this Symmetra PX500 UPS Display configurations has enabled SNMP v1 for monitoring via the DCE-server.

The essence of the bug #2: after the Display and NMC2 board many times lose/restore communication with the MIM and RIM of this UPS, for some unknown reason in the display settings SNMP v1 is disabled. This registers the DCE-server as a communication loss with Virtual Display.

In addition, after these many times lose/restore communication in the settings of the NMC2 board, you can see this about the Virtual Display settings:

Someone can confirm the presence of this bug, because I was tired every two months enabled SNMP v1 in the Virtual Display settings.

Very thanks for the support.

(CID:122693419)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
  • NMC
  • symmetra
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:22 PM

0 Likes
1
436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-03 06:22 PM

This answer was originally posted on DCIM Support by Valentin Kozlov on 2017-07-26


HI!

Loosing communication with MIM and RIM is abnormal operation mode. Probably it's hardware problem.

I guess nobody has test NMC settings reaction on abnormal operation.

I believe that this problem will be resolved after fixing communication lost issue. 

(CID:122694026)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:22 PM

In response to DCIM_Support
0 Likes
0
436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-03 06:22 PM

This comment was originally posted on DCIM Support by spezialist on 2017-07-26


Hi Valentin Kozlov,

Thanks for the feedback: I also created a support case with the number 41012099 for this issue. Therefore, it is necessary to wait for an answer with a possible solution to this problem...

Very thanks for the support.

(CID:123340420)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:22 PM

0 Likes
0
436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-03 06:22 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Share
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.