DCE failed backup - alarm configuration

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE failed backup - alarm configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

0 Likes
4
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

DCE failed backup - alarm configuration

Hello to all the professionals

Is there a way that we can get an active alarm (or any other alarm) for a failed DCE backup?

For example, when DCE backup fails at night, i want to get an alarm at this window in DCO :

 

just like we get alarms for temperature or humidity issues.

Thanks!

(CID:137732055)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

Dear sheep,

Sorry, but this is not possible.

In short, the current DCE-7.x software sends email notifications about of failed backup only to DCE administrators (if the correct email addresses have been entered in System -> User and Device Group Access...).

This type of notification is not subject to any DCE notification policies. This, if you want, such a DCE-7.x appliances design πŸ˜€.

If you have more questions, please ask.

With respect.

(CID:137732112)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

0 Likes
0
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

Dear sheep,

Sorry, but this is not possible.

In short, the current DCE-7.x software sends email notifications about of failed backup only to DCE administrators (if the correct email addresses have been entered in System -> User and Device Group Access...).

This type of notification is not subject to any DCE notification policies. This, if you want, such a DCE-7.x appliances design πŸ˜€.

If you have more questions, please ask.

With respect.

(CID:137732112)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

0 Likes
1
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

Hi sheep

Whilst @spezialist is correct, there might be a way to achieve what you want but I suspect it will not be trivial.

I'm happy to discuss with you if you wish

Cheers

Ed

(CID:137732244)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

In response to DCIM_Support
0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2024-04-03 11:12 PM

Hi Ed,

Thanks, i'll be happy to hear about this option.

Can we talk in private maybe?

 

Thanks

Sheep.

(CID:138807360)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2023-10-22 01:24 AM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 04:03 PM . Last Modified: β€Ž2023-10-22 01:24 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore