I know it has been some time since this post was created, but wanted to get a response out there in case other came across a similar issue.
From my experience I do not recommend a global scanning internal of 1 minute. For APC devices I recommend using priority scanning, which is a method where the APC device sends a request to DCE to poll it when an alarm goes active on the end-device. If the alarm is active at the time the polling occurs, then DCE would get the alarm and do the necessary actions with in. This option does not exist for 3rd party devices.
I would also suggest reaching out to technical support so that they can investigate the logs as well to see what is going on your server and/or desktop client.