EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 09:48 PM . Last Modified: β2024-04-03 12:41 AM
Good day
Please assist,
We are changing the Snmp settings however we need to know if the PDU will drop the current load - servers that are connect, would the servers connected to the PDU loose power ?
DCE - 7.4.1. PDU v3 AP7953 & AP7855A
Kind regards
(CID:148342945)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 09:48 PM . Last Modified: β2024-04-03 12:41 AM
Hi Juice,
Changing settings on the Network Management Card (NMC) may reboot the card itself but will not change the outlet states.
Thanks,
Steve
(CID:148342956)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 09:48 PM . Last Modified: β2024-04-03 12:41 AM
Hi Juice,
Changing settings on the Network Management Card (NMC) may reboot the card itself but will not change the outlet states.
Thanks,
Steve
(CID:148342956)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 09:48 PM . Last Modified: β2023-10-22 01:19 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.