Hi Team,
can you please confirm which specific ports need to open for DEC and for APC devices form firewall server, The customer wanted to disable some of the ports on their network and want to ensure the DCE will not be affected.
(CID:105462071)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:01 PM . Last Modified: 2024-04-09 01:16 AM
Hi Ali,
I think the "FA158328" contains the description for ports used on DCE, here is a copy/paste from the document:
The following outlines ports used and their application on any DCE Server:
Note: Ports or Protocols preceded by * can be changed from their default port number.
Incoming:
Port 80 (TCP/UDP) - *HTTP Communication from NetBotz Appliances / *ISX Central Console/Web API and 3rd party integrations.
*Port 443 (TCP) - HTTPS Communication from NetBotz Appliances / ISX Central Console
*Port 161(UDP), 162 (TCP/UDP)- SNMP Communication from SNMP Agent
*Port 502 (TCP/UDP)- Modbus TCP Communication from Modbus Device/Gateway Outgoing:
Port 80 (TCP/UDP)- *HTTP Communication to NetBotz Appliances / *ISX Central Console / HTTP Post to Web Server/Web API and
3rd party integrations.
*Port 443 (TCP) - HTTPS Communication to NetBotz Appliances / ISX Central Console
*Port 161 (UDP), 162(TCP/UDP) - SNMP Communication to SNMP Agent
*Port 25 (TCP)- SMTP Communication to Email Server
Port 21 (TCP)- FTP Communication to FTP Server
Port 123 (UDP)- NTP Communication to NTP Server
Port 139 (TCP/UDP)- SMB Communication to NAS / SAN
Port 53 (TCP/UDP)- DNS Communication to DNS Server
Port 111 (TCP)- NFS Mount
Port 2049 (UDP)- NFS Communication to NAS / SAN
Port 6000 (TCP)- APC Proprietary Communications protocol for use with AP76xx outlet strips and gen1 PDU on private lan.
Port 445 (TCP)- CIFS Communication to NAS / SAN
Port 502 (TCP/UDP)- Modbus TCP output to Building Management System
*Port 389(TCP/UDP)- Active Directory/LDAP
Kind regards
(CID:105462081)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:01 PM . Last Modified: 2024-04-09 01:16 AM
Hi Ali,
I think the "FA158328" contains the description for ports used on DCE, here is a copy/paste from the document:
The following outlines ports used and their application on any DCE Server:
Note: Ports or Protocols preceded by * can be changed from their default port number.
Incoming:
Port 80 (TCP/UDP) - *HTTP Communication from NetBotz Appliances / *ISX Central Console/Web API and 3rd party integrations.
*Port 443 (TCP) - HTTPS Communication from NetBotz Appliances / ISX Central Console
*Port 161(UDP), 162 (TCP/UDP)- SNMP Communication from SNMP Agent
*Port 502 (TCP/UDP)- Modbus TCP Communication from Modbus Device/Gateway Outgoing:
Port 80 (TCP/UDP)- *HTTP Communication to NetBotz Appliances / *ISX Central Console / HTTP Post to Web Server/Web API and
3rd party integrations.
*Port 443 (TCP) - HTTPS Communication to NetBotz Appliances / ISX Central Console
*Port 161 (UDP), 162(TCP/UDP) - SNMP Communication to SNMP Agent
*Port 25 (TCP)- SMTP Communication to Email Server
Port 21 (TCP)- FTP Communication to FTP Server
Port 123 (UDP)- NTP Communication to NTP Server
Port 139 (TCP/UDP)- SMB Communication to NAS / SAN
Port 53 (TCP/UDP)- DNS Communication to DNS Server
Port 111 (TCP)- NFS Mount
Port 2049 (UDP)- NFS Communication to NAS / SAN
Port 6000 (TCP)- APC Proprietary Communications protocol for use with AP76xx outlet strips and gen1 PDU on private lan.
Port 445 (TCP)- CIFS Communication to NAS / SAN
Port 502 (TCP/UDP)- Modbus TCP output to Building Management System
*Port 389(TCP/UDP)- Active Directory/LDAP
Kind regards
(CID:105462081)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:01 PM . Last Modified: 2024-04-09 01:16 AM
Thanks jef
(CID:105462098)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:01 PM . Last Modified: 2024-04-09 01:15 AM
The port information is listed here on our support website on the StruxureWare Data Center Expert Security Webpage: http://dcimsupport.apc.com/display/public/UADCE725/StruxureWare+Data+Center+Expert+Security#Struxure...
(CID:105462110)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:01 PM . Last Modified: 2024-04-09 01:15 AM
Thanks cory
(CID:105462118)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:01 PM . Last Modified: 2023-10-31 10:28 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.