DCE Network Management Systems Integration notification delay

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE Network Management Systems Integration notification delay
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
63
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

0 Likes
4
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

DCE Network Management Systems Integration notification delay

Hi Team,

is there anyway to delay the send of traps using the Network Management Systems Integration?

We have a project with sites around the world, and due to the latency in some circuits, DCE detects a lot of "Communication Status Offline alarm" per day. So all these alarms are sent and in less than five minutes they dissapear.

With Notification policies using "netbotz.mib" we can delay the send, but we would like to use "Powernet.mib".

Regards

 

(CID:131336752)

Labels
  • Labels:
  • Data Center Expert
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

0 Likes
2
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

Hi Javier,

That would have to be done at the threshold level and for SNMP and modbus devices, there is no option for a delay in the default communications threshold:

 

If you don't want to see these alerts at all, you could change their severity and in the NMS integration configuration, remove the lower level severities from being sent:

 

The only other option I can think for you to try would be to disable the offending thresholds and recreate them as thresholds for state for time. You can create thresholds for multiple devices at once and maybe even test them before you go system wide. Create an "other state threshold and choose state for time:

Click next and as long as they have a communications status sensor:

You can con configure a lost comm to alarm after a certain amount of time...here I put in 500 seconds or 10 minutes:

Different devices may or may not have this sensor and you may need to play around with it.

 

As you've seen, there is no option to delay NMS integration traps across the board and the easiest and recommended way around your issue other than fixing the reason for the lost comm issues is to use the alarm action /trap which uses the NetBotz MIB OIDs.

 

Steve.

 

 

 

 

 

 

(CID:131336794)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

In response to DCIM_Support
0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

Thank you Steve,

with the NetBotz MIB OIDs do we have the same details in the trap as we have with the PowernetMib?

I have read this document and analyzed the Netbotz mib and it seems that is easier to understand the traps if we use the Powernet mib:

https://www.schneider-electric.us/en/faqs/FA231439/

 

(CID:131336816)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

In response to DCIM_Support
0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2024-04-04 11:56 PM

Hi Javier,

Yes, for the most part the information is the same. You may also want to look at this k-base as well:

https://www.schneider-electric.us/en/faqs/FA236815

 

Steve

(CID:131336822)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2023-10-22 01:18 AM

0 Likes
0
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:22 PM . Last Modified: ‎2023-10-22 01:18 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of