Hi,
Is there somewhere I can download an up to date MIB file for DCE v7.2.6?
(Not the PowerNet MIB)
For the purpose of forwarding SNMP traps from, and scanning the DCE server directly
Thanks,
David
(CID:96764395)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:37 PM . Last Modified: 2024-04-09 11:47 PM
Hi David,
You can poll DCE directly using SNMP but you will only get a few CentOS based sysoids. You can not gather any data specific to DCE itself or the devices being monitored.
As for traps, there are 2 ways to set them up. If you configure an alert action for a sensor, the traps you receive will be based on the NetBotz Mib file. If you have any NetBotz devices, you get the same traps from them and the MIB can be downloaded directly from the device. See K-Base FA158368.
If you configure the NMS integration where DCE sends traps for any alert, you will receive traps based on the APC powernet mib which can be downloaded from www.apcc.com/tools/download. K-base FA231439 outlines this info. K-base itself is here:
http://www.apc.com/site/support/us/en/faq/
Steve
(CID:96764465)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:37 PM . Last Modified: 2024-04-09 11:47 PM
Hi David,
You can poll DCE directly using SNMP but you will only get a few CentOS based sysoids. You can not gather any data specific to DCE itself or the devices being monitored.
As for traps, there are 2 ways to set them up. If you configure an alert action for a sensor, the traps you receive will be based on the NetBotz Mib file. If you have any NetBotz devices, you get the same traps from them and the MIB can be downloaded directly from the device. See K-Base FA158368.
If you configure the NMS integration where DCE sends traps for any alert, you will receive traps based on the APC powernet mib which can be downloaded from www.apcc.com/tools/download. K-base FA231439 outlines this info. K-base itself is here:
http://www.apc.com/site/support/us/en/faq/
Steve
(CID:96764465)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:37 PM . Last Modified: 2024-04-09 11:47 PM
Hi Steve, Thanks for this info, this is helpful David
(CID:96764529)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:37 PM . Last Modified: 2023-10-31 10:27 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.