Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

DCE Alerts

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE Alerts
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
76
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:48 PM

0 Likes
4
365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 04:48 PM

DCE Alerts

This question was originally posted on DCIM Support by Tafadzwa Madyegasva on 2019-02-04


I have created a policy on DCE to send out Email and SMS Alerts received from Netbotz 250s, 455s and 550s however I can only get Alerts from the Netbotzs 250s because I can add the devices to the Policy. Any advice now how I can get DCE to send Alerts from the other Netbotz? For now I have created Virtual Sensors from the Netbotz 550s and 455s and added them into the policy.

(CID:139691699)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:48 PM

0 Likes
2
365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 04:48 PM

This answer was originally posted on DCIM Support by spezialist on 2019-02-04


Dear Tafadzwa Madyegasva,

From your question:

...Any advice now how I can get DCE to send Alerts from the other Netbotz? For now I have created Virtual Sensors from the Netbotz 550s and 455s and added them into the policy.

Creating DCE virtual sensors for NetBotz-4.x appliances is the right workaround, but only for temperature/humidity sensors. To understand why this is done this way, Steven Marchetti answer from the topic  will help you:

The NetBotz version 2 and 3 appliances (not the NB200 or AP9361 rack access) were designed on the old NetBotz and NetBotz Central paradigm. This design was based on the idea of the intelligence "on the edge".  This was so that there would be no single point of failure. If DCE goes down or loses comm with one or more devices, the devices themselves will still be able to alert for themselves. 

 

 Keep in mind that the NetBotz appliance is also able to alert in many more ways than DCE such as output relays etc. Leaving DCE alone to alert would cause the loss of this type of alerting mechanism.  Requests such as this have however come to our attention in the past and product management is aware that some customers would rather have DCE alert as it does for SNMP devices that it monitors. This is something that they may consider in the future but as far as I know, there are no current plans to change the way 7.x DCE and current NetBotz offerings work together.

See also about this my answer in the topic .

With respect.

(CID:139691772)

See Answer In Context

Reply
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:48 PM

0 Likes
2
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 04:48 PM

This answer was originally posted on DCIM Support by spezialist on 2019-02-04


Dear Tafadzwa Madyegasva,

From your question:

...Any advice now how I can get DCE to send Alerts from the other Netbotz? For now I have created Virtual Sensors from the Netbotz 550s and 455s and added them into the policy.

Creating DCE virtual sensors for NetBotz-4.x appliances is the right workaround, but only for temperature/humidity sensors. To understand why this is done this way, Steven Marchetti answer from the topic  will help you:

The NetBotz version 2 and 3 appliances (not the NB200 or AP9361 rack access) were designed on the old NetBotz and NetBotz Central paradigm. This design was based on the idea of the intelligence "on the edge".  This was so that there would be no single point of failure. If DCE goes down or loses comm with one or more devices, the devices themselves will still be able to alert for themselves. 

 

 Keep in mind that the NetBotz appliance is also able to alert in many more ways than DCE such as output relays etc. Leaving DCE alone to alert would cause the loss of this type of alerting mechanism.  Requests such as this have however come to our attention in the past and product management is aware that some customers would rather have DCE alert as it does for SNMP devices that it monitors. This is something that they may consider in the future but as far as I know, there are no current plans to change the way 7.x DCE and current NetBotz offerings work together.

See also about this my answer in the topic .

With respect.

(CID:139691772)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:48 PM

In response to DCIM_Support
0 Likes
0
365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 04:48 PM

This comment was originally posted on DCIM Support by Tafadzwa Madyegasva on 2019-02-04


Dear spezialist

Thank you for the Feedback. I will stick to the workaround for now.

(CID:139691791)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:49 PM

In response to DCIM_Support
0 Likes
0
365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 04:49 PM

This comment was originally posted on DCIM Support by spezialist on 2019-02-04


Ok, thanks for the good feedback 😀.

(CID:139691797)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:49 PM

0 Likes
0
367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 04:49 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc