Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84808members
354265posts

DCE Alerts

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
DCIM_Support
Picard
Picard
0 Likes
4
304

DCE Alerts

This question was originally posted on DCIM Support by Tafadzwa Madyegasva on 2019-02-04


I have created a policy on DCE to send out Email and SMS Alerts received from Netbotz 250s, 455s and 550s however I can only get Alerts from the Netbotzs 250s because I can add the devices to the Policy. Any advice now how I can get DCE to send Alerts from the other Netbotz? For now I have created Virtual Sensors from the Netbotz 550s and 455s and added them into the policy.

(CID:139691699)


Accepted Solutions
DCIM_Support
Picard
Picard
0 Likes
2
304

Re: DCE Alerts

This answer was originally posted on DCIM Support by spezialist on 2019-02-04


Dear Tafadzwa Madyegasva,

From your question:

...Any advice now how I can get DCE to send Alerts from the other Netbotz? For now I have created Virtual Sensors from the Netbotz 550s and 455s and added them into the policy.

Creating DCE virtual sensors for NetBotz-4.x appliances is the right workaround, but only for temperature/humidity sensors. To understand why this is done this way, Steven Marchetti answer from the topic  will help you:

The NetBotz version 2 and 3 appliances (not the NB200 or AP9361 rack access) were designed on the old NetBotz and NetBotz Central paradigm. This design was based on the idea of the intelligence "on the edge".  This was so that there would be no single point of failure. If DCE goes down or loses comm with one or more devices, the devices themselves will still be able to alert for themselves. 

 

 Keep in mind that the NetBotz appliance is also able to alert in many more ways than DCE such as output relays etc. Leaving DCE alone to alert would cause the loss of this type of alerting mechanism.  Requests such as this have however come to our attention in the past and product management is aware that some customers would rather have DCE alert as it does for SNMP devices that it monitors. This is something that they may consider in the future but as far as I know, there are no current plans to change the way 7.x DCE and current NetBotz offerings work together.

See also about this my answer in the topic .

With respect.

(CID:139691772)

See Answer In Context

4 Replies 4
DCIM_Support
Picard
Picard
0 Likes
2
305

Re: DCE Alerts

This answer was originally posted on DCIM Support by spezialist on 2019-02-04


Dear Tafadzwa Madyegasva,

From your question:

...Any advice now how I can get DCE to send Alerts from the other Netbotz? For now I have created Virtual Sensors from the Netbotz 550s and 455s and added them into the policy.

Creating DCE virtual sensors for NetBotz-4.x appliances is the right workaround, but only for temperature/humidity sensors. To understand why this is done this way, Steven Marchetti answer from the topic  will help you:

The NetBotz version 2 and 3 appliances (not the NB200 or AP9361 rack access) were designed on the old NetBotz and NetBotz Central paradigm. This design was based on the idea of the intelligence "on the edge".  This was so that there would be no single point of failure. If DCE goes down or loses comm with one or more devices, the devices themselves will still be able to alert for themselves. 

 

 Keep in mind that the NetBotz appliance is also able to alert in many more ways than DCE such as output relays etc. Leaving DCE alone to alert would cause the loss of this type of alerting mechanism.  Requests such as this have however come to our attention in the past and product management is aware that some customers would rather have DCE alert as it does for SNMP devices that it monitors. This is something that they may consider in the future but as far as I know, there are no current plans to change the way 7.x DCE and current NetBotz offerings work together.

See also about this my answer in the topic .

With respect.

(CID:139691772)

DCIM_Support
Picard
Picard
0 Likes
0
304

Re: DCE Alerts

This comment was originally posted on DCIM Support by Tafadzwa Madyegasva on 2019-02-04


Dear spezialist

Thank you for the Feedback. I will stick to the workaround for now.

(CID:139691791)

DCIM_Support
Picard
Picard
0 Likes
0
304

Re: DCE Alerts

This comment was originally posted on DCIM Support by spezialist on 2019-02-04


Ok, thanks for the good feedback 😀.

(CID:139691797)