DCE-7.7.1: "No Sensor History Available" to display a graph on the web-GUI!

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE-7.7.1: "No Sensor History Available" to display a graph on the web-GUI!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
8
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

DCE-7.7.1: "No Sensor History Available" to display a graph on the web-GUI!

Dear support,

It seems, that once again I discovered a bug in the new version of DCE-7.7.1 ☹️.

The essence of the bug: regardless of the web browser, if you tap on the preview of the sensor in the device, an empty graph window opens, which says that No Sensor History Available. For example, here is a browser window with a list of UPS sensors:

Then I tap on the sensor underlined in red (only for example, a similar problem with all sensors of all devices) and I get an empty graph window:

I emphasize, that a similar bug was discovered by me on several independent DCE-servers after upgrading to DCE-7.7.1.

This is very bad ☹️, and I hope that this bug will be fixed in the near future.

Very thanks for the support.

P.S.: I was somewhat confused when I saw, that starting with DCE-7.7.1, the DCE-client software is now only 64-bit (for both MS Windows and Linux OS).

(CID:148771781)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

Dear support,

I am glad to report, that in the new version of DCE-7.8.0 above the specified bug has been fixed 😀.

Very thanks for the support.

(CID:152569605)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

Support case number: 63221956.

(CID:148771790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

I am also experiencing the same issue.  Has there been any resolution to this yet?

(CID:149785208)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

My group is also now experiencing this after upgrading to 7.7.1.    This will cause great pain with upper management when it comes time to produce reports and screenshots that they request every month for particular devices for trending purposes.

 

(CID:149786868)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

It does seem that the sensor data is still being collected it is just not getting pulled into the webpage(s).  I say this as I do get up to 8 days worth of trending for the sensors when using the EcoStruxure IT app on my phone or tablet but that still does not give me a workable solution as I need to provide to my leadership trending of particular sensors for the prior month that I in the past was able to screenshot and include in the monthly reports.  Such as what I have included in this reply 

(CID:149787129)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

Here is a sample of the 8 days I am currently able to get from the EcoStructure IT app on my phone/tablet

(CID:149787134)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

In talking with the DCE Tech Support we did some more checking and within the actual DCE Client application (the standalone client) instead of the web based interface that I could actually produce a needed sensor "trending" graph that our upper management requires that I produce for them.  I was also able to confirm that my sensor data is still growing so information is in fact still being collected and stored.    I also opened a case on this : Schneider Electric Case #: 64289846

(CID:150241530)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

0 Likes
0
1530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2024-04-03 12:31 AM

Dear support,

I am glad to report, that in the new version of DCE-7.8.0 above the specified bug has been fixed 😀.

Very thanks for the support.

(CID:152569605)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2023-10-22 01:13 AM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:18 PM . Last Modified: ‎2023-10-22 01:13 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore