Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

0 Likes
8
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

DCE 7.5.0 - APC SNMP Device Configuration problem: "Not Retrieved"

Hi, 

I want to update the Date & Time using SNMP Device Configuration,

However, I have a problem when I tried to configure few PDUs:

Under the column - Last Retrieved appears "Not Retrieved (in red color)"

Moreover, I have to do not mark in the hostname checkbox in order to

continue to Configure Device Settings.

What can I do to fix this?

Great appreciation

 

(CID:153551060)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

0 Likes
6
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

Hi,

I'm just another user who had similar problem in the past. It was related to blocked firewall ports/protocols especially where DCE wants to send configuration to the device (21 or 22).

See more details here: 

StruxureWare Data Center Expert Security

(CID:153551172)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

Hi friend,

 

Tank you for the help, but the problem is not blocked firewall and

I noticed that the problem appears on a specific model AP8853: 32A-1PH.

Do you have this model?

 

Great appreciation

 

(CID:153551800)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

Dear sheep,

Can you show a screenshot of the firmware version from the web-GUI of your problematic AP8853 rPDUs?

With respect.

(CID:153551879)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

HI,

The firmware version:

Rack PDU: 6.5.6 

APC OS(AOS): 6.5.6

Boot Monitor: 6.5.6

With respect.

 

(CID:153552066)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

Dear sheep,

Maybe you should try updating one or two of the above rPDUs to the latest version v.6.8.2 and see the result?

Also, what is your version of DCE software?

With respect.

(CID:153552518)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

HI,

The version of DCE software: 7.5.0.62

I will try update to v.6.8.2 can you please send my a link for download?

But I have a lot of other PDUs with this version 6.5.6 that work great without any problem.

Important notice: the problem that I have is with a specific

model AP8853: 32A-1PH.

Maybe the problem is with this controller version?

 

 

With respect.

(CID:153552538)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2024-04-02 11:31 PM

Dear sheep,

Unfortunately, I could not find the web-links for the download ☹️. But you can download the latest DCE device firmware catalog, import it into DCE software, and from there update your problematic rPDUs.

I also have many rPDUs of AP8853 and AP8881, all with the latest firmware v.6.8.2. And I did not observe any problems on them.

Hope this helps you.

With respect.

(CID:153552743)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2023-10-22 01:11 AM

0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:34 AM . Last Modified: ‎2023-10-22 01:11 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore