Connect Netbotz to Struxureware via Modbus TCP

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Connect Netbotz to Struxureware via Modbus TCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
3
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Connect Netbotz to Struxureware via Modbus TCP

Hello.

I am trying to use a NetBotz rack monitor NBRK0570 as Modbus slave and share temperature and humidity data to a Struxureware AS-P server via Modbus TCP for BMS applications.

I have enabled TCP/IP communication and generated Slave ID for rack and pods.

 

However, when I use a Modbus Scanner for to read the Modbus Map than NetBotz Advanced View gave me, all values I get are 57005 (0xDEAD).

Anyone know why I can´t get the correct values? Should I change another configuration, or something else? Or NetBotz is not useful for Modbus TCP communications if is not used with Data Expert?

 

Thank you!

(CID:149785217)

Labels
  • Labels:
  • NetBotz
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
0
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Hi Gabriel,

 

I've enabled modbus over TCP on my 450. It's similar to the 570 but I didn't have anything connected to it for a quick test:

Then I set up the internal sensor pod as slave 1 and gave the few sensors registers:

Here are my settings using modbuspoll:

I'm getting responses. 0/1 are zero and 2/3 are zero because those are valid values for no smoke and off. 4/5 are 0 (less than 35565 on a 2x 16bit register) and 237 because 74.7 degrees in F is equal to 23.7 C. 

The rest are -8531 (0xDEAD) because that is the output the bot gives if that register is invalid or disabled.

Perhaps you don't have the output enabled?

What version of firmware are you running? I'm at 4.6.4.

The rest is pretty simple, you appear to have the slave and register map configured...I can't speak about the BMS.

 

Steve

 

 

(CID:149785244)

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
0
1043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Hi Gabriel,

 

I've enabled modbus over TCP on my 450. It's similar to the 570 but I didn't have anything connected to it for a quick test:

Then I set up the internal sensor pod as slave 1 and gave the few sensors registers:

Here are my settings using modbuspoll:

I'm getting responses. 0/1 are zero and 2/3 are zero because those are valid values for no smoke and off. 4/5 are 0 (less than 35565 on a 2x 16bit register) and 237 because 74.7 degrees in F is equal to 23.7 C. 

The rest are -8531 (0xDEAD) because that is the output the bot gives if that register is invalid or disabled.

Perhaps you don't have the output enabled?

What version of firmware are you running? I'm at 4.6.4.

The rest is pretty simple, you appear to have the slave and register map configured...I can't speak about the BMS.

 

Steve

 

 

(CID:149785244)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
0
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Hi, 

Try to read holding register 04 then address 31030? The modbus address should be 331030. 

 

Best Regards, 

 

TJ

(CID:149785387)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2023-10-20 05:09 AM

0 Likes
0
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2023-10-20 05:09 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of