Configuring BotzWare 4.6.1 to email to Office365

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Configuring BotzWare 4.6.1 to email to Office365
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

0 Likes
6
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

Configuring BotzWare 4.6.1 to email to Office365

Hi all. I am trying to get a NetBotz 570 to email out to Office365. I read Microsoft's website, they say point the email to smtp.office365.com on port 587 and enable TLS. Botzware version is 4.6.1 has a bunch of SSL options but no TLS. I'm stuck.

(CID:131960990)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

0 Likes
4
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

Dear Jon Vandenberg,

Very possibly, you will be helped by the web-link https://support.office.com/en-ie/article/How-to-set-up-a-multifunction-device-or-application-to-send..., which was published in post DCE Support for Office365 email . The post is addressed to DCE software, but it will probably be useful for configuring NetBotz-4.x appliances.

In addition, I highly recommend that you update the firmware of your NetBotz-4.x appliance to the latest version 4.6.2 of December 2017.

I hope this helps you.

With respect.

(CID:131961070)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

0 Likes
4
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

Dear Jon Vandenberg,

Very possibly, you will be helped by the web-link https://support.office.com/en-ie/article/How-to-set-up-a-multifunction-device-or-application-to-send..., which was published in post DCE Support for Office365 email . The post is addressed to DCE software, but it will probably be useful for configuring NetBotz-4.x appliances.

In addition, I highly recommend that you update the firmware of your NetBotz-4.x appliance to the latest version 4.6.2 of December 2017.

I hope this helps you.

With respect.

(CID:131961070)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

In response to DCIM_Support
0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

Hi, I can't find where on the APC website to download 4.6.2. Under the NBRK0570 for software and firmware it only goes up to 4.6.1. There are release notes for 4.6.2 but no download.

Also the SMTP settings that I am having trouble with come from the web link you provided. For Office365;

Server/smart host

smtp.office365.com

Port

Port 587 (recommended) or port 25

TLS/ StartTLS

Enabled

 

The problem is the NetBotz 570 (4.6.1) doesn't appear to support TLS, it only supports SSL.

(CID:131963019)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

In response to DCIM_Support
0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

Dear Jon Vandenberg,

The latest NetBotz-4.x firmware can be found here on EcoStruxure IT on page User Assistance for NetBotz v4.x under Downloads and documentation.

...The problem is the NetBotz 570 (4.6.1) doesn't appear to support TLS, it only supports SSL.

That's why I doubt if the above link from the Microsoft website will help you... Here, for example, a screenshot of my NetBotz-450 with the latest firmware v4.6.2:

As can be clearly seen - there is no mention of TLS encryption ☹️.

If you have any further questions, please ask.

With respect.

(CID:131963024)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

In response to DCIM_Support
0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

Dear Jon Vandenberg,

See also the outdated, but still relevant post  on a similar topic.

With respect.

(CID:131963022)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

In response to DCIM_Support
0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:44 PM . Last Modified: ‎2024-04-04 11:48 PM

Hi Jon,

 

TLS is enabled in the SSL functionality of the NetBotz e-mail routine. There is no specific setting that can be enabled or disabled for this.

 

Steve

(CID:131963118)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2023-10-20 05:09 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2023-10-20 05:09 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore