Configuration Power Supply for UPS in ITA 9.2.4

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Configuration Power Supply for UPS in ITA 9.2.4
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All
Related Products
product field
Schneider Electric
EcoStruxure IT Design CFD

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
SonNG
Ensign SonNG
Ensign

Posted: ‎2022-09-13 02:14 AM

0 Likes
12
3518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-13 02:14 AM

Configuration Power Supply for UPS in ITA 9.2.4

Hi Support Team,

 

I am facing a problem when configuring power supply for my 02 UPS. There doesn't seem to be an option in the properties section

5. Power supply config.PNG

Then when configuring PUE. The power supply is taken from the power meters of the 2 EMSB input cabinets. IT load I got from UPS connected with load bank to show capacity (No IT equipment yet). but the calculated value of PUE is not displayed

1.PNG2.PNG

 

I tried creating a value and assigning it. As a result, the PUE calculation is displayed. So am I doing something wrong?

3.PNG4.PNG

Labels
  • Labels:
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
SonNG
Ensign SonNG
Ensign

Posted: ‎2022-09-14 12:01 AM

0 Likes
0
3490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 12:01 AM

Hi team,

Can someone please help me with the answer?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Admiral Jef Admiral
Admiral

Posted: ‎2022-09-14 01:09 AM . Last Modified: ‎2022-09-14 01:20 AM

0 Likes
9
3477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 01:09 AM . Last Modified: ‎2022-09-14 01:20 AM

Hi SonNG,

 

In ITA currently supported option for power configuration is:
UPS -> PDU -> rack pdu -> rack-mounted assets

or 

PDU -> rack pdu -> rack-mounted assets

So basically, we cannot model power path upstream to UPS. You might want to use the UPS's properties setting just to make a note that it is connected to some sort of power supply/generator. 

 

And concerning the PUE calculations, I guess (only guessing) there might be delay in retrieving/reporting sensor data and/or PUE calculation updates. The displayed PUE doesn't appear to have the expected value (it is way to high, probably displaying the result of the previously entered data). In general, if there should be problem getting the sensor data (from DCE) and/or having unexpected data, then the PUE calculation(s) may fail.

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SonNG
Ensign SonNG
Ensign

Posted: ‎2022-09-14 03:24 AM

In response to Jef
0 Likes
8
3469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 03:24 AM

Hi Jef,

 

As seen, we have 2 EMSB total electrical cabinet that will independently power 2 UPSs and other infrastructure devices such as: PAC,...


The problem here is that if the power supply for 2 UPSs is not configured, the power capacity will be miscalculated. Specifically, the power capacity will be the total of 2 EMSB cabinets and 2 UPS.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Admiral Jef Admiral
Admiral

Posted: ‎2022-09-14 03:48 AM . Last Modified: ‎2022-09-14 04:06 AM

In response to SonNG
0 Likes
7
3464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 03:48 AM . Last Modified: ‎2022-09-14 04:06 AM

Hi SonNG,

 

Thanks for the comment, I understand what you mean. Unfortunately modeling the electrical cabinets and/or other power generators is currently un-supported. Perhaps limitations (power limitations) can be set on the UPS level/units, since the power capacity calculations (in ITA) will start from the UPS.

 

Kind regards,

Jef 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SonNG
Ensign SonNG
Ensign

Posted: ‎2022-09-14 04:15 AM

In response to Jef
0 Likes
6
3455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 04:15 AM

Hi Jef,

 

So that means the power capacity is only calculated on the UPS.

 

In addition, other infrastructure equipment that consumes electricity will not be included in the power capacity.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Admiral Jef Admiral
Admiral

Posted: ‎2022-09-14 04:25 AM

In response to SonNG
0 Likes
5
3448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 04:25 AM

Hi SonNG,

 

Not only calculated on the UPS itself, but also downstream from the UPS, eg. it will be calculated on the connected PDU and rack pdus.

 

as a test try to change the power capacity on a UPS (properties > Power > Capacity) and then see the power capacity changes in power tool-tip (in Power overlay, hover over a UPS, PDU, rack, etc.)

 

Kind regards,

Jef

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SonNG
Ensign SonNG
Ensign

Posted: ‎2022-09-14 07:02 AM

In response to Jef
0 Likes
4
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 07:02 AM

Hi Jef,

 

As I understand it the power capacity will be calculated on the UPS and from the connections to the UPS eg PDU and Rack PDU.


In addition, other infrastructure devices such as PAC, if not connected to power from the UPS, will not be able to calculate the power capacity.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Admiral Jef Admiral
Admiral

Posted: ‎2022-09-14 11:16 PM

In response to SonNG
0 Likes
3
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 11:16 PM

Hi SonNG,

 

That's correct, equipment that are not included in a power path will not be involved in power capacity calculations.

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SonNG
Ensign SonNG
Ensign

Posted: ‎2022-09-14 11:42 PM

In response to Jef
0 Likes
2
3415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-14 11:42 PM

Hi Jef

 

Thanks for the Support.

 

SonNG

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Admiral Jef Admiral
Admiral

Posted: ‎2022-09-15 12:30 AM

In response to SonNG
0 Likes
1
3408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-15 12:30 AM

Hi SonNG,

 

My pleasure,

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Lt. Commander Tafadzwa
Lt. Commander

Posted: ‎2023-03-31 06:26 AM

In response to Jef
0 Likes
0
2605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-31 06:26 AM

Hi @Jef 

 

I wish to find out if this has been changed in ITA v 9.3.4. I want to configure a Power Path Starting from the Distribution Board Level that feeds the UPS and also feeds Cooling Units in the DC. Following your conversation I understand Power Paths can only be dsigned starting from the UPS and everything else that is not on UPS Power cannot be included when calculating PUE?

 

Regards.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2023-03-31 06:42 AM

0 Likes
0
2600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-31 06:42 AM

You can create power path above the UPS and for other infrastructure like cooling units in ITA.  However you cannot connect the UPS to anything upstream of it. ITA Capacity still only sees the UPS as the start of the power path and bases a majority of it's power capacity calculations of UPS capacity/loading.  


Calculating PUE works differently, if you use the native ITA PUE/DCiE dashboard as mentioned in this post, you can add either static values or measured values from DCE for facilties load and IT load.  We also have another ITA module, Energy Efficiency which you can use to calculate PUE/DCiE for multiple sites with much more complex PUE calculations using java script and outside data sources.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore