Hi All,
I was wondering if anyone knows how to change the IP on an AP7611 PDU. This type of PDU is discontinued and I can't find the user manual online.
One of my Field Service Engineers is on site servicing these units.
(CID:99156916)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:03 PM . Last Modified: 2024-04-09 04:19 AM
Hi William, thanks for posting. There might be a delay in addressing this issue as a few of our customer support Team members are on holiday. Stay tuned!
(CID:99156933)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:03 PM . Last Modified: 2024-04-09 04:18 AM
Hi William,
This is one of the older PDUs that communicates using the DCAL protocol. You may recall the vertical gray PDUs that also used this protocol. The only way to IP these devices is to put them on the private LAN for either DCE with DHCP enabled or ISX Manager. They wil lget IPs automatically. they can't be IPd manually.
Steve
(CID:99156974)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:04 PM . Last Modified: 2023-10-31 10:20 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.