EcoStruxure IT forum
A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.
Posted: 2020-07-04 03:36 AM
This question was originally posted on DCIM Support by Javier Zurera on 2018-01-12
Hello team,
we have an issue with the capacity overview in a deployment over DCO 8.2.
We have different locations, and in the global view for Scotland we see this capacity overview:
But inside Scotland we only have one floor plan for Glasgow with this capacity:
So both Capacity Overviews should be the same, shouldn't they?
Then inside Glasgow, we have 4 rooms:
Main Room with two small UPSs A-B that feed two in-row cooling machines for a high density area. Each UPS is 40 kW, total in this room: 80 kW
Also in this Main Room we have two rectifiers, A-B, with 2.4 kW each one. Total 5 kW
Room UPS-A with a 540 kW UPS
Room UPS-B with a 540 kW UPS
Another room only with racks.
So, the total capacity of Scotland is 1.165 kW (80+5+540+540).
But we have defined 2N redundancy in all the racks, so we expected to see the half of the total capacity, 582,5 kW for this site.
Where are the errors?
Thanks in advance.
(CID:128061637)
Posted: 2020-07-04 03:36 AM
This answer was originally posted on DCIM Support by Christopherus Laurentius on 2018-01-15
Two things, while waiting for the rest to feedback.
(CID:128061982)
Posted: 2020-07-04 03:37 AM
This answer was originally posted on DCIM Support by Calum McCulloch on 2018-01-15
Hi Javier
I had added 3 new cabinets which caused the 4000kW + increase in reported power, I don't know how it was so much, but I deleted them and both figures are now the same.
(CID:128062460)
Posted: 2020-07-04 03:37 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.